what is the diffrence between current transformer and
voltage trasformer
Answer Posted / naresh
Current Transformer is a device used to measure the current
of high value in the lines,by connecting the device in
series with the line.
voltage transformer is also an indicating device which is
used to measure the potential across the line.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
for 11KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV UG system what will be typical per KM "R" "L" "C" parameter.
what are the necessary basic electrical topics to learn for mechanical engineer to deal practical problems.
explain types of electric welding and its applications
WHAT IS THE DIFFERENCE BETWEEN AN ACB & mccb 7 WHAT IS THE CRITERIA WHEN TO USE WHICH OF THE TWO
distribution is maximum done by a)radial b)network c) parallel d)b & c
what transformer we used normally and upto which kva?
what is arc flash and what are the hazards involved
What is online and offline ups? how does it works?
what are the usual topology of transformers at different substations in the power system and why that particular topology is choosen. what are the limitaions of that topology?
what are the parameters plays a major role in Potential transformer Burden calculation??
In an ACB shunt trip coil and undervoltage coil operated normally( breaker open and charged). But closing coil not operating untill manually discharge and recharging. Any help.
Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?
what is meant by surge? what we called for high currents?
Explain what cmos is and its benefits?
WHAT IS THE CURRENT CARRYING CAPACITY OF 2.5/3 CORE HI TUFF CABLE,WILL IT SAFLEY CARRY 8.6 AMPS OVER 120 METRES,CAN YOU ALSO ANSWER WITH FORMULA FOR WORKINGS OUT ,THANK YOU 3RDYR APPRENTICE.