What is the difference between online ups and offline ups?

Answer Posted / martin

Online UPS is the one which gives output all the time from
battery whether there is power failure or power on. You
get backing from battery all the time.

Offline UPS supplies Mains to the output when power supply
is regular and charges batteries as well at the same time.
When power fails it switches those batteries to produce
output for power backup.

Is This Answer Correct ?    157 Yes 29 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain

987


How to check the cable fault / hv test of transformer cable.

1424


CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415

2262


what happend to DC shunt motor if its field winding insulation becomes slightly weak? will that motor can run on full load or not explain in detail. thanks

1185


what are factors comes under relay setting (distance relay 7sa52) under OPEN DELTA VTs connection??

2129






What it the purpose of parallel phasing transfomers??

1530


Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.

1279


Define end float in a motor?

5489


what is the transformer turn ratio formula and give some examples?

1942


Why need 3phase machine double earthing?

1347


whit is 33kv power 300*300 cable full current with formula

1403


Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?

4647


Grid fault level [KA]?

2227


what is the difference between fault current ant short circuit current?

2277


How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?

1524