What is the difference between 2 wires RTD's and 3 wires
RTD's.Kindly explain the wiring diagram.

Answer Posted / dale bergemann

RTD is Resistance Temperature Detector. It will change resistance at its leads when the sensor is exposed to changing temperature. They are commonly found in windings of motors or surfaces of bearings or immersed in liquid to produce a resistance when converted by a monitoring device can indicate degrees in the medium it is placed.
A lead wire is place on each side of the sensor and the resistance can be measured across those two leads, commonly Red and White in color. Because it measures ohms, the value will be affected by the length of the leads, which will 'bias' the reading and convert incorrectly. To address this, a third wire can be added in parallel with the white wire. Now the monitor measures the resistance between and R & W and compensates it with the resistance measured between the two white wires. Now we have the true resistance change of the sensor, without the error caused by lead length.
They also make 4 wire RTDs which have two Red and two White leads to further enhance capability and increase accuracy by analyzing in a bridge fashion.

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

can any one tell me about the Extra low voltage systems?From where we give supply to these type of systems??

1526


What is dynamo function in DG sets and draw block diagram?

1599


which stabilizer is better ? AVR, Servo Stabilizer, Static stabilizer etc & why explain it

2424


what will happen if frequency is below 50 hz?

1577


What is true sine wave or pure sine wave inverter?? Is it sine wave or step wave?? If it is step wave, waves with how much step is considered as pure sine wave? Is it possible to produce pure sinewave using power electronics?

1391






What is control system?

743


What is the Load Capacity of Panther conductor (0.2) and dog conductor (0.2) 

2328


a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5

1190


How can we measure earthing resistance test (Earth meggar) of Transformer neutral pit while in live condition?.

1645


Write the force balance equation of ideal dashpot element.

857


What is the difference between the relay and the circuit breaker?

624


how many single tension hardware are required on a double circuit transmission tower?

1484


What is open delta Xformer? It's adavntages & Use?

1791


What is the polarization index value ? (Pi value)and simple definition of polarization index ?

776


how much cable size required for 70 kilowatt load.