How flow control valve is working with pnuematic positioner
and I/P convreter from command is given from remote

Answer Posted / carl_ellis

A controller (the remote device) generates an electronic
4-20mA output signal which tells the valve what its position
should be.

The 4-20mA signal is an input to an I/P
(current-to-pneumatic) transducer, which creates a pneumatic
output signal proportional to the 4-20mA electronic signal
from the controller, probably a 3-15psi pneumatic signal.

The pneumatic control signal is an input to the pneumatic
positioner, which mechanically senses the valve's position.
The positioner drives the actuator with as much supply air
pressure as is necessary to drive the valve to position
demanded by the control signal.

Carl Ellis
Measure First

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how many types of spped sensors n vibration sensors?their basic principle n connection?

2089


We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.

1148


applications of plc in printing and packaging?

1686


Galvanizing.

1480


Calibration procedure for water rotameters

1762






why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.

2217


when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??

1726


what is loop1 and loop2 in MTS LT?

4200


how to design orifice plate?what is the equation?

1638


what is thermo coupler and how it works

5009


Which language of programing is popular? how can i learn it ?

1722


What is instrumentation control?

661


how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.

1586


Please tell me details about Sox,Nox,SWAS analyser????

3295


WHAT IS THE DIFF. BETWEEN SKIN TEMPERATURE AND PASSES TEMPERATURE..?