Do you know how to measure the earth resistance? if so
explain it
Answer Posted / ahmad abu alrob
Normally no meaning for earth resistance, we use a
measurement of resistance in a definite location to
calculate the Earth Resistivity which can be used for the
calculation of Grounding/ Earthing mesh resistance.
Measurement can be done in one of the following:
1- Normal Volt/ Ampere method: Inject current and measure
voltage , then you will got the resistance.
OR
2- Wenner method using 4 electrodes: You should use the
equipment especially used for this purpose, and you should
follow the instruction attached with the equipment.
OR
3- Using Schlumberger method applying 4 electrodes: same
equipment used in 2 but different calculation applied.
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
draw the block diagram of fire alarm?
Why High voltage are generate noise ?
what is per unit calculation?looking for simple and strong explanation thk u
how to calculate earth fault relay current and CBCT ratio
what is mean by NPS (Negative phase sequence)fault? what is the difference between EFR & OCR faults?
How Can you do Maintenance of ACB of 2000Amperes
The shot circuit in any winding of transformer result? Explain
What is excitation in case of dc motor?
why we setting 95 deg and 105 deg in wti and oti of distibution transformer ? give the reson for that ?
State and define norton’s theorem?
What is the feedback in the control system?
how the phase convertor changes the no. of phases
difference between main metering kiosk and check metering kiosk
what is the difference between switch yard to residential area.and how much required it.
how to avoid Saturation in C.T?