How can calculate ups battery back up time?
Answer Posted / yogesh
UPS backup time= Ah of battery * no of battery/output kva * 130
| Is This Answer Correct ? | 73 Yes | 68 No |
Post New Answer View All Answers
can anyone please help me to find the rupturing or breaking capacity in KA of circuit breaker (MCCB,VCB,ACB etc) of HT and LT side of a distribution transformer...please help with detailed step by step answer...thank you
How a capacitor discharge weld power supply works? what is the use of a pulse transformer?
Draw a 230kv two-bus bar system showing the following. 1.Two generators (150MW) each connected through one 15.75/230KV transformers 2. 1 outgoing lines 3. Two 230/130 KV transformers 4. BUS PT's 5. CT
what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.
Single phase and threephase power calculation
What are dcs and plc?
The series field winding has low resistance while the shunt field winding has high resistance. Why?
What is difference between start imitation and start interlock for 3 phase motor protection ?
explain the types of drives
Block diagram of Power line communication?
in shunt clippers why a resistor is used in sereis with the input
we have 3 single phase transformers. how will we generate 6 supply from 3 phase supply input
What is the minimum value of hfe for the oscillations in transistorized rc phase shift oscillator?
hai iam arunkumar. i have applied for an section enginner in rrb. i want lat 5 years solved question papers. if u have please sedn it to arun30682@gmail.com
how to meas-our losses for L.T & H.T