As per my knowledge, Indoor package substation refers to
GIS (Gas Insulated Switchgear) substation whereas in
outdoos substation we go for AIS (Air insulated
switchgear/circuit breakers). Also, GIS substation is much
more compact as compared to AIS/Otdoor substation.
| Is This Answer Correct ? | 6 Yes | 12 No |