what is the difference between star and delta connection ?
when we use each one ?what is the best ?
Answer Posted / zahid khan
star is only used intial to because the supply voltage is
VL/root3 and due to high starting torque of induction
motor,'star delta circut used above 20kw.
| Is This Answer Correct ? | 29 Yes | 13 No |
Post New Answer View All Answers
what work will do diffrential realay DG set
how much excitation voltage required to generate 1mw power?
explain types of electric welding and its applications
how to select the double earth conductor if 21A full load?
how many parameters can integrate with fire alarm basically ?
For a 6.6kV Motor it is recommended to do megger test with 500 V d.c and not more than 5kV d.c but the Hi voltage withstand test should be performed by 12kV AC. Why the dc voltage test should be limited but AC voltage withstand test could be with such a high voltage?
How to calculate earth wire load by formula
How do u analyse protection fault when vcb tripping on load
anyone please send transformer parameter design formulas & details of tap changer ? plz i have interview this week its more helpful for me ?
What are the disadvantages of hydropower?
Can I use distributon class/transmission class Lightning arresots for protecting the building? If not why please explain?
What is the suitable transmission voltage?
describe the Tranformer testing procedure
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
how do you test tachos and servos