Do you know how to measure the earth resistance? if so
explain it

Answer Posted / k.viswanathan

Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.

In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.

The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm

Is This Answer Correct ?    55 Yes 12 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?

2477


What is the current carrying capacity of 0SWG,3SWG,10 & 12 SWG solid bare overhead copper conductors?

2965


how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?

2515


How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?

3637


How cmd is calculated in case of energy neters

1382






What is process of anneling transformer core

1469


What do you mean by the zone of protection?

627


internally connection of photvoltic module

1461


use of choke in APFC panels

4895


what is PDU in transformer?? which company manufacture??

1382


Practical condition in 400KV Sub station:- Breaker(open) , isolator(open), Earthing (close) at both end e.g A & B. Now Open A Stn Earthing than Open B stn Earthing (Which have a 50MVA reactor) , AND suddenly show R,Y,B phase 704KV,573KV,118KV respectively. Que is without closing of breaker how it is possible.???? My Whats app No:07621840498 for Further Discussion. Pls experts suggest.

1598


I have 2 KW electric water heater.I am gonna use it in controlling water temp.so I needed to increase or decrease the heating capacity.is there any electrical-electronic circuit for varying the resistance & so current?

2587


i want to know that what is the eligibility critaria for ongc exam?

2569


What is the instrument to check the rotating diode fuse of alternator in running conditions?

2016


what is the sludge current

1566