What are the different protection systems used to protect
the transformer internally and externally?
Answer Posted / venkat iyer
1) Differential Protection
2) Winding Temp
3) oil Temp
4) Under Voltage and over voltage
5) Under Frequncy Protection for Higher Range of Power
Transformers
6) Bucholz Relay Protection for oil cooled transformers (to
detect incipient fault)
7) Pressure reilef Valve for oil cooled transformers
8) Restricted Earth Fault Protection
9) Overload, short circuit and earth fault protection
10) Protection against fire in case of oil cooled
transformers
11) directional protection
Is This Answer Correct ? | 12 Yes | 2 No |
Post New Answer View All Answers
what is method for testing CT
what is the use of the puls transformer in UPS & how it works???????????
Single phase and threephase power calculation
Where servomechanism is used?
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
What are the advantages of autotransformer?
Dear sir, my knowledge about cable size determination is limited. Though I read examples I could not calculate the Cable size required for electric driven pump 40 KW, 380 Volt, 50 HZ, 50 meter from transformer and it is three phase star delta starting. Please help as there is no one in my surroundings to help.
As a electrical engineer.. what are the basic norms should follow in transformer oil testing.. 1.What is the Electrode type? 2.How long time you will give for oil testing?
what is diff. between earthing grid,earthing mess, earting grid?
tell me about eletrical contractor
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
What is dielectric loss?
when elecromagnatic waves are propogated in a wave guide?
how solar power plant energy meter multiplication factor
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)