How to make position transmitter feedback reverse i.e at
valve close i want 20ma output and at full open 4ma.for the
NELES positioner,model:ND8261/TS1.
Answers were Sorted based on User's Feedback
Answer / guest
removed link from actuator than fix back which condition
you need you will get other wise if you have HART base
change your counter (first read counter ) than increased
from potentio meter you can? i donot have idies about same
your positioner model but you can try
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / shabeerali
1. Reverse the potentiometer wire connection of position
transmitter.
2. Perform calibration. if required adjust zero and span .
then position transmitter gives reverse feed back
For direct feedback brown, red, orange.
for Reverse feedback orange, red, brown.
pls refer the manual
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kiraninst
If there is PLC/ Dcs then simply change the gain for reverse -1/ reverse action
| Is This Answer Correct ? | 0 Yes | 0 No |
What are difference between automatic and manual control system?
what's the criteria of using over range protector when installing Pressure Gauge
why 4ma show higher zero ? i have transmiter flow renge 0-1000 m3/h but 4 ma show in monitoring 200 m3/h and 20 ma show 1000 m3/h i want when 4ma show 0 m3/h and 20ma 1000m3/h
What is difference b/w absolute & gauge pressure? EXPLAIN
What will the new flow factor if D/P Transmitter is RE-RANGED from 25" WC to 50" WC
Full form of KKS when use DCS.
how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)
1)What is the suitable MOC for flow meters working at temperature between 200 - 250 cen. 2)In which application the mass flow meters are not advisable 3)Is it advisable to use radiation type or radar type instrument for non contact application
Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?
what is diffrence between cascade & three element system.
why generation of syncronized generator increases when frequency of grid is less then 50Hz & generation decreases when grid frequency goes up from 50 Hz, as comparision with set value entered in govering panel?
if we have 450 mm heigth boiler drum level ,so what is span & zero value for a dpt tranmitter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)