Answer / ramji
The differential protection is used for protecting the
transformer from internal winding fault,internal winding
shorts etc.,.It operates through three sets of CT's
connected in and out of transformer.It may or may not
operate during minor earth faults.REF is used to detect the
earth fault at restricted zone where its protection CT is
connected.It will surely operate during earth fault.But not
in windings short.
Is This Answer Correct ? | 31 Yes | 4 No |
Answer / gunasekaran
both are using for internal fault but differential
protection only sensitive up to 92% winding of the
transformer if any fault occur in balance 8% winding diff is
not operating so we r using REF protection
Is This Answer Correct ? | 11 Yes | 7 No |
Answer / nikhil thakkar
REF and Differential both pritection are for internal zone and SEF for external zone. Actual all protections are voltage/current/power based and they are back to each other. DIFFERENTIAL AND REF both protection is for internal fault i.e trafo winding . differential sense unbalance between both end of trafo. /Gen. . REF sense unbalance caused between NCT and phase CTdue to earth fault abd actual backup for REF is SEF.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ashish
as per my knowledge ref protections hav to be assigned
separately on both sides of traffo it protects 90% of
winding.
it is unit protection and its very sensitive.
while talking about diff protection two cts in each phase
on both sides of trafo is there any diff in incoming and
outgoing current will leads to trip so both are equally
required.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / raveendra nath
Differential protection provides excellent protection for
phase- to-phase and most phase - to - earth faults, this
element is less sensitive for single- phase-to-earth faults
close to the earth point in solidly earthed transformers.
For these faults (i.e fault at transformer winding turns
nearer to neutral point ), phase current changes very
little, but large current flows in the neutral.
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / gunasekaran
at internal earth fault condition diffrentional sensitive
only 85% only remaining 15% covered by REF protection
Is This Answer Correct ? | 1 Yes | 8 No |
Answer / munish
REF 64T is used for protect the 95% winding of T/F.it sens
only the internal fault of T/F and 51NT circulating earth
fault relay used for detect the other area.
87T diff. is act only when the difference B/W both side
current is more than setting value
Is This Answer Correct ? | 0 Yes | 8 No |
what is meant by transformer differential protection ?
in dc shunt motor if field winding is shorted then
A 3 phase motor, 440 voltage, induction motor. If we take out rotor from motor and if we give supply 440 volt to stator then what happens?????
Is better to supply the voltage for static exciter from the auxiliary power source or from the SG terminals? And why?
What is the physical significant of power factor?
how can a race around condition be eliminated using master slave flipflop?????
diffrence between alternating and pulsating field?
what is difference between sub-station and switch yard.
What is Difference Between static & Dynamic Pressure of Fan & Blowers
we have two 11/.433 kv. distribution Transformer rating as 1000 kva & 500 kva , i wants to run parallel both transformer. both transformer impendence voltage is 5.24%, How can we run both t/f, & how sharing the load
Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.
Why CT secondary should not left open??????????