Which instrument used to calibrate the pressure switch?
Answers were Sorted based on User's Feedback
Answer / vijay vaidya
pressure calibrator or dead weight tester
Is This Answer Correct ? | 19 Yes | 3 No |
Answer / biswarup das
Answer 1 and 2 is absolutely right .
another way is to use comparison tester.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / g.paden
druck pressure calibrator and dead weight tester
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / s.arun raja
For Pressure Switch Calibration Should be need Comparison
Pressure Test Pump and We Can't use Dead Weight Pressure
Guage Tester , Because Pressure Switch We Should Calibrate
Raising or falling Method and for Nc/No Checking need
Continuity Tester or multimeter.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / b0nz0
Referring to the previous answers, a deadweight tester
should not be used as it is only accurate when the weights
are 'floating'.
It is much better to use a Druck or comparator as the
pressure can be varied above and below the setpoint.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / samir patel
any type of dead weight tester,multifunction pressure
calibrator,multimeter
Is This Answer Correct ? | 0 Yes | 1 No |
How we can check the 2 wire proxy switch? & how it is connected to DI MODULE OF PLC?
Give an example where you had aproblem on the job, and tell me how you solved the problem. and the finalvoutcome.
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
calibration of instruments.
what is LAS in foundation fieldbus protocol?
what is the difference between signal cable and ontrol cable?
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?
key phaser where is use and work
How many mode are in ups?
What is the detail function of I/O card in DCS ? Why we dont use the I/O directly with controller?
Explain , how timer based pneumatic control valve will work ?
What is the difference between HMI,SCADA and MMI,not abbrevation?