what are the standard values for resistances(Megger testing)
between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
Answer / pswin
You ask the value between L,N and E. So I will assume that you will test for single phase and the test voltage must be 500 v scale and full scale is 100 mega ohm.Minimum value should be 0.5 mega ohm between each conductors. If lower than that value, the cable or wire is not certified to use. For three phase, above answer is acceptable,too.
Is This Answer Correct ? | 16 Yes | 3 No |
It is being often experienced that due to single phasing fault of any source transmission line of any closed loop synchronized circuit all the power transformers with primary stared trips but the power transformer with primary delta wont, why ?
What is the difference between voltages or potential difference? And what are they?
how calculate cable size in squre mm, when the load is given by in kw? do u have current rating chart of elctrical cables?
what is a synchronizing lamp ?
What is mean by sinewave.
how to calculate the slowness and fastness of energy meter if we have different kw load for example (0.746 kw and meter rev constant 400 and we calculate the 2 rev in 30 sec) please explain the formula thanks
1 Answers WAPDA Water and Power Development Authority,
Why heat produce in AC machine higher than DC machine?
how to find three phase complex power in per unit and MVA?
How do we calculate the Out put voltage of generator, after the excitation is being given?
What is the Efficiency in Electric motor ?
What will happend if given Vfd out put to step up transformer
how to use single phase supply for a three phase equipement.