Answer / rajender mohan
The Busbar Rating specifies the maximum short circuit current it can see and operate, so you can put a breaker up to breaking capacity of busbar,
Ambience temprature has to taken into consideration while designing the LT Panel.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / opselvaraj
Not neceesary but it is preferable to have the same rating
from operation/maintenance point of view.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / anil jangra
KA rating of any switchgear is depending on fault level of connecting load,so it necessary to calculate the fault current of load than select the switchgear rating,as per my opinion the must be able to clear the fault without damaging it self and healty one feeder also.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pravin deshbhratar
yes, whatever fault current rating that we are maintaining
for the Incomer breaker same has to be maintained for
outgoing breaker also unless there is a stepdown
transformer in line. Because the fault level is calculated
on the basis of actual load of the substation that it is
going to carry out, so it is suggested that we have to use
the same KA ratiing for Incomer as well as the Outgoing
breaker.
Is This Answer Correct ? | 1 Yes | 4 No |
Not Necessary,depend upon your system means you are going
to use same KA rating for reactive power or normal power.if
you are using for reactive power then you hava to have same
KA rating of BB.however, you can check for normal load.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / r.gunasekaran
Circuit breaker KA rating should be more than that bus bar
KA.
Is This Answer Correct ? | 0 Yes | 4 No |
What is the basic principle of operation of alternators/dc generators?
sir what is the purpose of SF6 in HT breaker and what is the pressure should be maintain in the breaker?
What is thresh hold value of current?
is it value of power factor is more than unit. whats effects in the source supply
Did RMU have ct and pt ?
HOW TO BUILD THE SINGLE PHASE TO THREE PHASE CONVERTER? CAN PROVIDE ME CIRCUIT..THANKS
WHAT IS ELECTRICAL MAINTAINTENCE ?
what is the function of buchhos rely in transformer
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
for 500mw power production how many range of transformer set in unit please reply if three transformer use .
what is frequency transformer?
Differnce between earthing and nuetral