Answer / rajender mohan
The Busbar Rating specifies the maximum short circuit current it can see and operate, so you can put a breaker up to breaking capacity of busbar,
Ambience temprature has to taken into consideration while designing the LT Panel.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / opselvaraj
Not neceesary but it is preferable to have the same rating
from operation/maintenance point of view.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / anil jangra
KA rating of any switchgear is depending on fault level of connecting load,so it necessary to calculate the fault current of load than select the switchgear rating,as per my opinion the must be able to clear the fault without damaging it self and healty one feeder also.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pravin deshbhratar
yes, whatever fault current rating that we are maintaining
for the Incomer breaker same has to be maintained for
outgoing breaker also unless there is a stepdown
transformer in line. Because the fault level is calculated
on the basis of actual load of the substation that it is
going to carry out, so it is suggested that we have to use
the same KA ratiing for Incomer as well as the Outgoing
breaker.
| Is This Answer Correct ? | 1 Yes | 4 No |
Not Necessary,depend upon your system means you are going
to use same KA rating for reactive power or normal power.if
you are using for reactive power then you hava to have same
KA rating of BB.however, you can check for normal load.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / r.gunasekaran
Circuit breaker KA rating should be more than that bus bar
KA.
| Is This Answer Correct ? | 0 Yes | 4 No |
A parallel flow heat exchanger will perform better than a counter flow heat exchanger. State if the statement is true or false.
what is Dog conductor? wasp conductor? rabbit conductor? ant conductor?
what is the difference between a hooter and a mcp
how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you
What is synchro?
How to design power source say 5KW i/p :415v 3 ph, o/p 5KW constant, variable currnt and variable volatge 10-230v,
What is Harmonics how it is produced and what is the method to control the same
Iin ESP why positive is grounded ? why not negative ?
for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???
why some harmonics are disturbing while the others not
difference btw neutral and ground?
What is the criteria for deciding whther fire wall is required between two power transformers
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)