IF i have switchgear with busbar current rating of 1000Amp
35kA then is it necessary to have outgoing breaker kA rating
to be equal to busbar kA rating?

Answers were Sorted based on User's Feedback



IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / rajender mohan

The Busbar Rating specifies the maximum short circuit current it can see and operate, so you can put a breaker up to breaking capacity of busbar,
Ambience temprature has to taken into consideration while designing the LT Panel.

Is This Answer Correct ?    3 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / opselvaraj

Not neceesary but it is preferable to have the same rating
from operation/maintenance point of view.

Is This Answer Correct ?    4 Yes 2 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / anil jangra

KA rating of any switchgear is depending on fault level of connecting load,so it necessary to calculate the fault current of load than select the switchgear rating,as per my opinion the must be able to clear the fault without damaging it self and healty one feeder also.

Is This Answer Correct ?    0 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / pravin deshbhratar

yes, whatever fault current rating that we are maintaining
for the Incomer breaker same has to be maintained for
outgoing breaker also unless there is a stepdown
transformer in line. Because the fault level is calculated
on the basis of actual load of the substation that it is
going to carry out, so it is suggested that we have to use
the same KA ratiing for Incomer as well as the Outgoing
breaker.

Is This Answer Correct ?    1 Yes 4 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / mohammad farman khan

Not Necessary,depend upon your system means you are going
to use same KA rating for reactive power or normal power.if
you are using for reactive power then you hava to have same
KA rating of BB.however, you can check for normal load.

Is This Answer Correct ?    0 Yes 3 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / r.gunasekaran

Circuit breaker KA rating should be more than that bus bar
KA.

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

What is the basic principle of operation of alternators/dc generators?

0 Answers  


sir what is the purpose of SF6 in HT breaker and what is the pressure should be maintain in the breaker?

2 Answers   Kirloskar,


What is thresh hold value of current?

0 Answers  


is it value of power factor is more than unit. whats effects in the source supply

0 Answers  


Did RMU have ct and pt ?

0 Answers  






HOW TO BUILD THE SINGLE PHASE TO THREE PHASE CONVERTER? CAN PROVIDE ME CIRCUIT..THANKS

0 Answers  


WHAT IS ELECTRICAL MAINTAINTENCE ?

0 Answers  


what is the function of buchhos rely in transformer

5 Answers  


what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.

1 Answers   ABB,


for 500mw power production how many range of transformer set in unit please reply if three transformer use .

2 Answers  


what is frequency transformer?

2 Answers  


Differnce between earthing and nuetral

3 Answers   S Tech, wbsedcl,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)