Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


IF i have switchgear with busbar current rating of 1000Amp
35kA then is it necessary to have outgoing breaker kA rating
to be equal to busbar kA rating?

Answers were Sorted based on User's Feedback



IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / rajender mohan

The Busbar Rating specifies the maximum short circuit current it can see and operate, so you can put a breaker up to breaking capacity of busbar,
Ambience temprature has to taken into consideration while designing the LT Panel.

Is This Answer Correct ?    3 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / opselvaraj

Not neceesary but it is preferable to have the same rating
from operation/maintenance point of view.

Is This Answer Correct ?    4 Yes 2 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / anil jangra

KA rating of any switchgear is depending on fault level of connecting load,so it necessary to calculate the fault current of load than select the switchgear rating,as per my opinion the must be able to clear the fault without damaging it self and healty one feeder also.

Is This Answer Correct ?    0 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / pravin deshbhratar

yes, whatever fault current rating that we are maintaining
for the Incomer breaker same has to be maintained for
outgoing breaker also unless there is a stepdown
transformer in line. Because the fault level is calculated
on the basis of actual load of the substation that it is
going to carry out, so it is suggested that we have to use
the same KA ratiing for Incomer as well as the Outgoing
breaker.

Is This Answer Correct ?    1 Yes 4 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / mohammad farman khan

Not Necessary,depend upon your system means you are going
to use same KA rating for reactive power or normal power.if
you are using for reactive power then you hava to have same
KA rating of BB.however, you can check for normal load.

Is This Answer Correct ?    0 Yes 3 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / r.gunasekaran

Circuit breaker KA rating should be more than that bus bar
KA.

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

A parallel flow heat exchanger will perform better than a counter flow heat exchanger. State if the statement is true or false.

0 Answers   Blue Star,


what is Dog conductor? wasp conductor? rabbit conductor? ant conductor?

3 Answers  


what is the difference between a hooter and a mcp

2 Answers  


how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you

0 Answers  


What is synchro?

0 Answers  


How to design power source say 5KW i/p :415v 3 ph, o/p 5KW constant, variable currnt and variable volatge 10-230v,

2 Answers  


What is Harmonics how it is produced and what is the method to control the same

0 Answers   Siemens,


Iin ESP why positive is grounded ? why not negative ?

0 Answers  


for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???

5 Answers   PowerTech,


why some harmonics are disturbing while the others not

1 Answers  


difference btw neutral and ground?

2 Answers   ERG,


What is the criteria for deciding whther fire wall is required between two power transformers

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)