Answer / ramji
First calculate the actual KVAR load.Then calculated the
actual PF.Then as per required PF, calculate the KVAR to be
added.This is the value of capacitor bank to be shunted.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / g parsaram reddy
capacitor bank selection base on the connected load
ex - 500kw load formula is kvar = kw ( tan cos-1pf) - (tan cos-1pf)there is power factor taken lower and higher valu , ex2 kvar= 250(tan cos-1 0.8)- (tan cos-1 0.96)step2 kvar=250(tan36.36-tan16.26) than 250(0.74-0.29) than250(0.45)than kvar=114.5this is required