Any one Give me formula for to increse the power factor,
0.8 to 0.95, How much the KVAr Required
Answers were Sorted based on User's Feedback
Answer / thowsif_emerson_csm team
Calculation of Required Kvar:-
Initial P.f-PFi , Desired P.f-PFd and Real Power of Load in
KW...
KVAR=KW(tanAi-tanAd)
where,
Ai=Cosinverse(PFi) = Initial Power Factor Angle.
Ad=Cosinverse(PFd) = Final Power Factor Angle.
For Example:-
PFi=.85 & PFd=0.9 & Real Load=50 KW
For this required KVAR is 6.7 KVAR....
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / thowsif_emerson_csm team
Hi Pls Provide me the following Details:-
Input Load in KW....
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / sonam sherpa
P.F = M.D*(Tan(cos-1 x)-Tan(cos-1 y))
M.D - max. demand.
x- Actual power factor
y- Required power factor
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sonam sherpa
in above formual P.F- Capacitor rating in Kvar
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / akhilesh singh
please go through V.K.Mehta's book (power system)
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sk rafiquil islam (kaithi,jamu
p=1.732*v*i*cos phaii so cos phai=p/(1.732*v*i) so,we can decrease of current we can developed pf
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ravi
Hi All,
Can u pls provide me the correct formula to calc.
P.f?????????????????
Is This Answer Correct ? | 1 Yes | 3 No |
In Which vector group power transformers are mostly manufactured?
how to calculate units consumption for a 12 hp motor /hr.
what is humming noise and wha is the reason to develop humming noise in a mv pannel ?
what is the aircraft voltage and frequency standard ?
I have experienced electrical maintenance HT ,but I completed be ECE ....can I apply c license or not ???? Pls help me friend s...
what is size of 3phase 4wire cable to be used for 11 ton ductable A.C and how to calculate cable size for different load
what is meant by armature reaction & where its happen ?
what is power factor? whether it should be high or low? why?
difference between ac and dc generators
Why we are not placing c.B 's btwn generator and transformer.? what happens when generator gets disconnected from transformer when it is running @ full load?
What are the disadvantages of LT AVR over HT AVR?
1 Answers APTransco, Jindal, TNEB Tamil Nadu Electricity Board,
Whatis the current capacity of 33KV/ 0.433KV transformer on Primary and secondary side/