Answer / www.pooneetkashyap.blogspot.co
from emf equation of X'mer
E=4.44fNAB (http://en.wikipedia.org/wiki/Transformer)
where E=voltage
f=frequency
A=Area
N=number of turns
B=magnetic flux density
in general we can say
A=E/(4.44fNB)
for constant value of E,N,B
if we increase F,then Area of core will decreases means size
of transformer will reduce.
| Is This Answer Correct ? | 123 Yes | 9 No |
Answer / satish kumar(satty)
EMF of a transformer increases with frequency. As a result the transformer can be physically more compact because a given core is able to transfer more power without reaching saturation and fewer turns are required to achieve the same impedance.
| Is This Answer Correct ? | 36 Yes | 10 No |
Answer / jaipal rathod
from transeformer eqn size of the transeformer is inversely proportional to the supply freqency...
e=4.44 f BA N
flux=B*A
SO,A=1/F
When freq increase,size or area of the t/f is decreased
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / chandan kumar
E=4.44bafn V
so if we increase the supply frequency the induced emf
increases
and the active power of transformer is given by P=VI,
SO POWER DEVELOPED IS INCREASES of the same t/f
if we increase the frequency
therefor the size is decreases
| Is This Answer Correct ? | 3 Yes | 6 No |
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
how synchronous condenser is used in place of synchronous generator with out negotiating IEEE standards? Can i use 3 generators as synchronous generators and 2 generators as a synchronous condensers in an IEEE 14 bus system with out disturbing the standards?
What is means by MacAdam Ellipse?
define digital electronic
What are the advantages of stationary armature and rotating field system?
What is the required value while doing the megering
Why PT is fitted in incomer panel.....?
How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.
direction of tarbine& genrator
what is the difference between the following 2 situations ? 1)Line & Neutral=240V Line & Earth=230V Neutral & Earth=10V 2)Line & Neutral=230V Line & Earth=240V Neutral & Earth=10V
Transformer rating=> 15/20 MVA.Why there are two raings? What should be the rating of the fuse at the secondary if the voltage level is 13.8KV/4.16KV?
why in 3.5 core means 3 core for phase and .5 for neutral?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)