after parallaing two generators current is shooting up in
both the generators.for ex: load is 400 kw..after paralling
and load sharing current in running gen is approx 900 amps
and incoming is 750 amps which is too high when trying
toshift the load current in incoming gen is coming more
than 1300 amps and both getting tripped and making
blackout..
Answers were Sorted based on User's Feedback
Answer / raj
Is both generator parallel to GRID means Your generator
AVR is not working properly, these requrired kvar sharing
must is there available or not If availabel AVR settings to
shoule be change then is not solved the problem it is
required winding test required.
Is This Answer Correct ? | 1 Yes | 0 No |
it looks like one of the genset is having a big difference in voltage or
the droop kit if fitted something wrong with it or
check after paralling do you have balanced three phase voltage and current or one of the phase is open circuit or
the gen is running the other as motor
if you know the actual reasons later please let us know also
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yuvi
This means that the phase angle of the existing generator
and the new incomming generator are not matching. You can
try the bright lamp or the dark lamp method to synk them.
There is no way in which you can directly plug in a
alternator to an active AC system.
Is This Answer Correct ? | 1 Yes | 1 No |
. The string effcy in AC sys is 80% Then for same power, the string effcy in dc sys is a) less than 80% b) 80% c) more than 80% d) zero
1 Answers Engineers India Limited,
Can anyone explain the power flow in flouresent lamps (tube lights) .What are the functions of Starter & choke used there?
what is active power & reactive power?
what is the difference between starter and control panel..?
why one side of tubelight glows after switch off ?
What shall be the secondary output voltage if the primary winding of a 220/6V, 50 Hz transformer is energized by an 110V, 60 Hz supply?
I would like to know that the fault curretn at base load and at 10% generation will be same? Fault level of BUS remain same with different generation?
How vaccum is formed to create a vaccum interrupter or anything related with vaccum?
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
IN bateery size of positive is biger than negative .why?
what instruments used for measuring of inductance and capacitance.