How to calculate CT ratio for 11KV 1500KVA Transformer
500KVA MD and 1400KVA connected load ?
Note:- As per MSEB(Maharastra state electricity Board)
Answer / k.prakashchandra
Max current based on Tr capacity is 79A. hence rated primary
current of ct would be 100A.If development is not expected 75 A
| Is This Answer Correct ? | 5 Yes | 3 No |
what is the slip of synchronous motor
What are the two major types of control system?
how can we detect that which is receiving side and which is sendind end of a trnasmmison line by just seiing it?i.e its which end is coming from genertaing and distribution side?
1.What is the proper definition of power system stability? 2.some times a blue spark is visible in the secondary side of a distribution transformer at the contact position of bushings and fuse wire,why?
i have three phase 25kva transformer but there is two phase line how can i connect to the two phase line?
What are steps to be taken while designing of DYN11 distribution transformer to achieve magnetising balance?
megger how much voltage will produce ?
can we ran equipment up to 10kw between phase to grounding/ earthing. beside above can we use grounding instead of neutral. .
1 Answers TNEB Tamil Nadu Electricity Board,
Dear, How much ph is maintained of water electrolite used in lrs for slipring induction motor ?
in domestic service connection,what is service main?
why substation are rated like 11KV or 33KV?
3 Answers TNEB Tamil Nadu Electricity Board,
How open delta used for protection?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)