Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / lokendra

dear friends
as per ISA standards 24 VDC is the minimum possible voltage
at which the spark will not come,we know our transmitters
will give max output current of 27 mA here they have limit
this current bcause the power we get is less than 1 watt
(P=VxI)648mW which is not capable of producing a spark thus
they have avoided spark generation by selecting 24 VDC and
limiting currnt to 27mA.this comes under extrisic safety.

Is This Answer Correct ?    47 Yes 6 No

Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / sivakumar

see all loop powered transmitters are capable of
withstanding 10 t0 36v dc ...as per the process requirement
it will vary.. insome industries they are using 12v dc
also.. 24 vdc is used because as per ISA there are some
standards wich will match other process reqirement like
24vdc relays for digital control also wecan use 24dc to
energize tis relays

Is This Answer Correct ?    10 Yes 6 No

Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / sagar

Because 24vdc is a minimum voltage where no possibilities of any kind of spark.
so we can prevent our costly instuments using 24 vdc.

Is This Answer Correct ?    6 Yes 2 No

Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / venkatesh

all transmitters(24vdc) are using for very imp parmeters , so the 24v dc coming from smps or any dc power units and these working with 230v ac UPS SUPPLY so if anytime some powertrips will come this transmitters still working with on ups supply with smps outputs

Is This Answer Correct ?    0 Yes 0 No

Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / maddy2504

It totally depends, 24 V DC 2 wire is not always applicable
every wehere some times it is 2 wire, 3 wire (2 cable for
power up & signal & 1 cable is for earthing), some times it
will 4 wire(2 for powerup & 2 for signal).

24 V Dc is for certain limit b'coz voltage will be drop in
that case w'll use 230v AC.

Is This Answer Correct ?    5 Yes 6 No

Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / abdul

Give extra power supply damage this device because standard instrument give standard electrical signal 4-20 and 24 V dc

Is This Answer Correct ?    0 Yes 1 No

Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / ankur gupta

it is not possible to design capacitors,resistors with
greater ratings.since size is the restriction.

Is This Answer Correct ?    6 Yes 15 No

Why 24VDC power Supply is used as standard for all loop powered transmitters?..

Answer / ln sharma

as per international standard.

Is This Answer Correct ?    9 Yes 29 No

Post New Answer

More Instrumentation Interview Questions

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500 ltr/hr.) what should i do?

9 Answers  


role of electrical engineer in the instrumentation industry

1 Answers  


-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.

0 Answers  


Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?

1 Answers  


What is PDS and PDMS ?

0 Answers  






Why the Proximitor supply should be Negative voltage? Why should not we give Positive voltage to the Transducer?

6 Answers   Moser Baer,


hydrogen purity meter calibrating and commissioning procedure can be explained?

1 Answers  


what are the different types of communication cables used in automation and what are the difference in the cables

1 Answers   KN,


A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe

0 Answers  


why 4 to 20 ma ,why not 0 to 20 or 3 to 15 or anything

19 Answers   Honeywell, TCS, TN,


i am working in thermal power plant . if temperature transmitter is not showing reading in dcs then how can we rectify the problem?

8 Answers   TATA,


I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?

0 Answers   SRAAC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)