Answer / vishal i vadodaria
As we know that in Y connection there are 3 phases [R,Y&B] & a neutral.
In neutral we provide a resistance & than we used to ground it.Such system called neutral ground resistance [NGR].
Why we use NGR?
AS we know ideally the sum of current Ir+Iy+Ib is zero. So in normal condition the current which flow through neutral of Y winding is very low.
In case of occurrence of phase to phase or phase to ground fault heavy unbalance current will be generated & that will flow through neutral. To restrict this current we provide a resistance in neutral.
If we do not provide resistance in neutral & fault occurs at that time a heavy current will flow & it cause excessive heating in stator winding & it may damage the winding. to prevent this we provided a resistance in neutral.
| Is This Answer Correct ? | 60 Yes | 9 No |
Answer / vrishali ajagaonkar
CRITERIA-IN ORDER TO PROTECT THE STATOR CORE FROM DAMAGE
DURING INTERNAL EARTH FAULT IT IS NECESSARY TO LIMIT THE
STATOR EARTH FAULT CURRENT AL LOW AS POSSIBLE.MAY BE UPTO
10AMP FOR GENERATOR.
BASIS FOR SELECTION OF NGTR-
IF GENERATOR IS CONNECTED TO THE SYSTEM THROUGH GENERATOR
TRANSFORMER THEN GENERATOR CAN BE TREATED AS AN ISOLATED
SYSTEM WHICH IS NOT INFLUENCED BY THE DISTRIBUTION EARTHING
SYSTEM. IN THIS CASE YOU CAN SELECT EARTH FAULT CURRENT AS
LOW AS POSSIBLE, BUT IF WE USE NGR THEN IN ORDER TO LIMIT
THE LOW EARTH FAULT CURRENT SIZE OF THE NGR WILL BE
INCREASED.DUE TO BIG SIZE OF NGR WE REQUIRED MORE SPACE &
ALSO ITS TOO COSTLY.
V = IR MEANS IF V CONSTANT I IS INVERSELY PROPORTIONAL TO R
EXP:-TO LIMIT 10AMP CURRENT , V =11KV/ROOT 3
R = 11/ROOT 3/10*1000=635.10 OHM ( VERY HIGH VALUE)
FOR OVERCOME ON THIS, GENERAL PRACTICE TO USE A NGTR SO THAT
WE CAN LIMIT LOW EARTH CURRENT WITHOUT ANY EXTRA COST.
EXP:- NGTR 11/240V
TO LIMIT 10AMP CURRENT
CURRENT REFLECT ON SECONDARY SIDE OF NGTR WILL BE
= (11000/ROOT 3/240)*10=264.6 AMP.
RESISTOR VALUE ON SECONDARY SIDE R =240/264.6 =0.9 OHM (
APPROXIMATELY) WHICH IS MUCH LOWER THAN 635.10 OHM.
BASIS FOR SELECTION OF NGR-
IF GENERATOR IS DIRECTLY CONNECTED TO THE SYSTEM THEN WE CAN
NOT LIMIT THE EARTH FAULT CURRENT UP TO 10 AMP. WE HAVE TO
SELECT THE EARTH FAULT CURRENT VALUE ABOVE THE RESIDUAL
CAPACITIVE CHARGING CURRENT OF SYSTEM.ALSO WE NEED TO CHECK
THE POSSIBILITY OF RELAY SETTING OPERATION WITH CT RATIO.
FOR EXMP- IF CT RATIO IS 2000/1AMP & EARTH FAULT LIMIT
CURRENT IS 100AMP RELAY SELECTED WITH 10 % SETTING.
THEN THAT RELAY WILL SEE ONLY 200AMP EARTH FAULT CURRENT IT
WILL NOT OPERATE ON 100AMP CURRENT.
ALSO WE CAN NOT KEEP GENERATOR SOLIDLY GROUNDED BECAUSE OF
HIGH EARTH FAULT CURRENT STATOR CAN DAMAGE SAME WILL HAPPEN
WITH HT MOTOR IF IT IS CONNECTED TO THIS SYSTEM.
SO FOR THIS CASE WE NEED TO SELECT THE NGR WITH PROPER EARTH
FAULT CURRENT ( ABOVE THE RESIDUAL CAPACITIVE CHARGING
CURRENT OF SYSTEM) TO AVOID UNWANTED TRIPPING.
| Is This Answer Correct ? | 44 Yes | 3 No |
ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?
Is it really necessary to have reactive power in transmission line to transfer the power from one place to other?
Why are calling leading power factor is a capacitive load?
what is the different between counterpoise earthing and pipe earthing?
what is the Pickup/drop off ratio in BCPU relays
Inductor and capacitor........power in one phase and ...... in it another phase.
What is the difference between IGBT and TRIAC?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
how can we change the rotating direction of single phase AC induction motors?
12 Answers Heubach Colour, L&T, MNM Jain Engineering College,
I PURCHASED A DEISEL GENARATOR SET OF AVR TYPE& RATING 125KVA BUT SOME TIMES THE OUTPUT VOLTAGE IS FLUCTUATING WHAT ARE THE PROBABLE REASONS GIVE ME
What does Bode plot tell you?
How to convert 110 volt alternating current to 12 volt direct current
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)