Answer / somnath sharma
The use of earth switches is to send any trapped charge in the line into ground after the line is switched off.
Mainly what happens, when the line is switched off, some charges remain trapped in line due to their own capacity and also due to influence of side by X-line. This trapped charge is dangerous if someone goes for maintenance of that very line. So it is very much required to neutralise that much charge and here comes the use of earth switches.
Is This Answer Correct ? | 196 Yes | 14 No |
earth switches used in substation . in that when isolator
OPEN condition earth switch is CLOSED. here any induction
that passes thro' earth switch to ground.when isolator in
CLOSED condition Earth switch should be Open
Is This Answer Correct ? | 68 Yes | 9 No |
Answer / mohammad
Earthing Switch is necessary to earth the conducting parts
before maintenance and also to provide deliberate
short-current while testing.This enables various tests to be
performed on the Switchgear or item of equipment, such as
testing the current Transformer of measuring the operating
time of breakers, without having to open the enclosure.
During normal operation the insulation is bypassed by a
short-circuit-proof link.
Is This Answer Correct ? | 28 Yes | 7 No |
How i can calculate the cable size for given load,there is any formula,for 3 phase and single phase
2 Answers Prescient Technologies,
want to know about DMRC
what is dc mator?types of dc motor?losses in dc motor?what is the mechanical,electrical and commercial efficiency of a dc motor?
why some harmonics are disturbing while the others not
Why Nutral CT rating for Earth Fault Protection of Transformer neutral shall be 20% of Full load Current of Transformer
what is sustainable current of any conductors . a bare busbar or pvc cable has different sustainable current .
how to convert kw in to unit
Does the electricity supply authority send its customers power (kW) or voltape (V)? Asked by Ivan Muliro
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
Does the total power means fundamental plus Harmonics?
electrical resistance in human body?please dedails quick. mail.psrinivasan20@yahoo.com
Mention the difference between Analogue and Digital circuit?