Answer / ashish khamparia
for C.T. rating we should have motor rating in kw. so that
we calculate the load.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / padmanabha prasad
CT range depends on the fullload current of the motor not
voltage. So first find out the motor FLA and based on that
u can select the range of CT(metering). Range should be 0
to FLA*20%)
| Is This Answer Correct ? | 4 Yes | 0 No |
We must know full load ampere of the motor.If we know ,we
can select C.T. as their ratio to show on ammeter. It is
best to use ammeter selector to know ampere on each phase.
| Is This Answer Correct ? | 2 Yes | 0 No |
Mr. Naresh: Motor rating is always kW and transformer rating is KVA.
Alternator no depends on power factor.
For CT design, Should be need KW & voltage lavel.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / peter desoza
P=1.732 VI X.85
= 1 amp APPROX
NO NEED CT, because the main purpose of CT is to step down
the current,U CAN USE SIMPLE AMPERE METER OK
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naresh
we should know the kva rating of the motor & also power
factor.
| Is This Answer Correct ? | 0 Yes | 1 No |
How PSV sizing being done
HARMONICS ARE ALWAYS IN INTEGER LIKE 2ND OR 3RD HARMONICS,NOT IN FRACTION LIKE 0.5 HARMONICS.....????????
what could be the reason of a burnt current transformer in an electrical panel
Explain principle of Soft-starter & how its working???
what is meant by distance protection ? how distance protection relay function ?
to calculate voltage drop of cable which current we consider that means full load current or panel size?
What is the function of RCBO? What are the different sensitivity ratings & each application?
WHAT IS MEANT BY DERATING OF THYRISTOR?
If we have two nodes A and B and Vab is the potential difference between these nodes then which node is called reference node a.node A b.node B c. Ground node
what is the control circuit for operating the clean room air shower
Require Generator Capcity ( KVA ) for 3 Phase Motor having 4.7Kw with starting current of 16amps?
What happened when we give 2 phase supply to a 1 phase equimpent. It's effect on equipment's efficiency and life?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)