why we r used APFC Panel in industrial area.when P.F. low
then wat will be the effect in our system?
Answers were Sorted based on User's Feedback
when power factor is unity,then industries receive active
power or useful power only i.e KW=KVA
If it is lagging PF,the industries receive both useful power
(KW) and reactive power(useless power)(KVAr).To meet this
reactive power, distribution transformer capacity also to
be increased.Then only we can avoid low voltage,losses
etc.
So we have to provide APFC panel to bring the pf to unity
Is This Answer Correct ? | 55 Yes | 4 No |
Answer / rajeev
APFC Panel is used to maintain the power factor near unity
by adding capacitance across the load.
P = V x I x Power factor.
100 = 100 x 1 x 1 ( Idle case)
If power factor decrease to 0.1
100 = 100 x 10 x 0.1
Here we can observe that current in circuit increased
from 1 amp to 10 amp with decrease in power factor from 1
to 0.1
This is the effect of low power factor in system. Due to
this increased current higher rating of cables , breakers
etc required. also due to this increased current we require
more power generated as MVA demand shoots up.
Is This Answer Correct ? | 31 Yes | 3 No |
Answer / surender singh
In industrial area's due to inductive loads the power factor
becomes low. As the PF low, the inductive power also becomes
low.To raise the power we use APFC Panel.
Is This Answer Correct ? | 25 Yes | 9 No |
Answer / umashankar
The ideal Power Factor (PF) is Unity or 1, but most
Industrial loads have a PF lower than 1. Moreover, this
lower PF is usually due to Inductive loads, arising out of
the windings of Transformers, Motors,etc. These loads
consume kVARs (the Wattless component) from the supply
line. The APFC supplies these kVARs via a capacitor located
close to the load, reducing the current drawn from the
supply line. For an Industry with dynamically changing
loads, Automatic PF Compensation affords the best Return on
Investment, since the kVAR investment required is smaller
than with fixed capacitors needed to meet the entire load.
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / kirti harinkhede
In industry most of the load is inductive in nature which
results in lagging power factor that is why there is loss
and wastage of energy which results in high power bills and
heavy penalties from electricity boards. If the load is
uneven it is very difficult to maintain unity power factor.
To overcome this difficulty APFC panel is used which
maintains unity P.F.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sunil.dutta
lower Power factor,s harms every one knows, but we use a
capacitor panel to confirm our p.f. not crossing limits
causing government penalty on lower p.f of plant.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / gautam makavana
What is the function of reactor in LT &HT Apfc panel ? And why it is used ?
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ramendra shukla
Automatic power factor correction Panels are used in
Industry for maintaining the power factor close by unity &
for reducing Reactive power component by the auto
functioning(with solid state device) of Capacitor Banks.
and by getting the Pf close to unit we will also get the
incentive(as per respective PF slab) from Energy providing
co.
In case of low pf it means the current is lagging behind
with voltage and we are having the reactive power in
syatem.So system will take more active than earlier.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vivek
if we increase the pf as unity we get healthy power and no harmonic present ion that system. so that losses is decreses and our equipment runs up to full efficiency. so that we reduce the tarrif.and finally save electricity save money..
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gunasekaran
kva=kw+kvar
apparant power is constant because our TR rating we cannot
alter so if KVAR is incress active power is decress so we
cannot use power for useful for that at the same time for
low PF it draw more currrent so we have to design the
appaliences for higher rating.
Is This Answer Correct ? | 2 Yes | 3 No |
why dc power can not be used in transformer?
33 Answers GE, Sail,
What happened when the field winding of dc series motor is open?
What is the difference between sensitive earth fault and restricted earth fault in power transformers?
Spacing of Transformers ratings are 10kva,15kva,25kva,63kva,110kva,150kva .........so on Q) Why transformer are not manufactured having ratings in between or other than these standard ratings ?
what will hapen if secodery circuit is open of current transformer WHy neutral to ground trips when neutral touches the ground
IF 3 NOS.OF HEATERS,3KW CAPACITY EACH,1 NO.HEATER CONNECTED IN R PHASE,1 IN Y PHASE AND 1 IN B PHASE.THEIR END POINTS CONNECTED IN STAR.IF I CONNECT THIS STAR POINT TO NEUTRAL OR DO NOT CONNECT TO NEUTRAL.WHAT WILL THE DIFFERENCE.
I Just want do EHS Certified Certification Distance Course From Govt approved,so can any body provide me details.
Brief use of isolation transformer & how it works.
Can we use 3 phase energy meter for measureing power in 2 phase 440 V phase circuit?
Why stones are layed under Transformer
what is the reason of battery voltage is 12v maintain?please answer me.mail-psrinivasan20@yahoo.com
) why transformer cannot rotate though the principle behind induction motor is similar to a transformer