How to calcute the cable size for both HT and LT please
specify the formula for that
Regards
Chethan C
Answer / kanchan dogra
Selection of HT cable is based on
1. short circuit calculation
2. Full load current capacity
1. Short Ckt. calculation
if total load is 3000 KVA, V 11 KV
short ckt MVA on HV side = 350 MVA (As per standard practice)
short ckt. current Ik= MVA/root3 x KV
350/root3 x 1= 18.4 KA
duration of short Ckt= 1 Second
cross section area of the conductor = Ik x root T/.094
18.4x root T/.094 = 95 SQ.mm
2. Full Load current
Total Load= 3000 KVA
System Voltage= 11 KV
Full load current = KVA/ root3 x KV
3000/root 3 x 11= 157 Amp.
derating factor = .7
current carrying capacity after derating = 157/.7 = 224.95 AMP.
Hence select cable for this current.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the differance between a converter duty transformer and normal power transformer?
why in transformers voltage given is in the multiple of 11
Pleae send me last 5 years of Question book about RRB chennai.
hot water tank,top element 240v across,the bottom 120v across,why?
what should be distance between phase to phase in 415v system?
How to size Air Circuit breaker (ACB)? What is the most important factors?
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
what is the mean of"turbo" in turbo alternator???
What is the use of IGBT in UPS & its working??????????
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases slip A does not alter B decreases C increases D none of above
What will hapen if we run generator below 47.6hz frequency?
What are operating procudures & Safety precautions to be observed while operating OLTC in manual mode ?