What are the steps for Testing of 6.6KV HT Panels?
Answers were Sorted based on User's Feedback
Answer / rajendran
The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel
| Is This Answer Correct ? | 62 Yes | 8 No |
Answer / rama raju (essar)
The following test are to be carried out for HT panels..
1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.
| Is This Answer Correct ? | 51 Yes | 2 No |
Answer / siva prasad
1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / c aaron franklin del
1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / sheikh rashid
Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.
www.berquetechnologies.com
berquetechnologies@gmail.com
| Is This Answer Correct ? | 9 Yes | 3 No |
what is the range of maximum DOL and SDS can be use for pump and fan application
At what factor resistance r of a conductor depends?
how we calculate the withstansing current capacity of wires&cables?
why wave traps are placed only at y and r phase?
what is laser diodes?
Why don't connect earth wire to elcb?if earth fault occur,how will detect it
1 Answers TATA, Tata Communications, Telecommunications,
Why distribution transformer secondary voltage is 0.433kV instead of 0.415kV.all other switchgear rating are 415 volt??
Which device is provided as backup of Buchholz relay???
What is The Resistance Formula
Why two main buses and one transfer bus scheme not using for 400kV switchyard
why the neutral point of star connnection oscillates?
What do you mean by screen of power cables?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)