What are the steps for Testing of 6.6KV HT Panels?
Answers were Sorted based on User's Feedback
Answer / rajendran
The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel
Is This Answer Correct ? | 62 Yes | 8 No |
Answer / rama raju (essar)
The following test are to be carried out for HT panels..
1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.
Is This Answer Correct ? | 51 Yes | 2 No |
Answer / siva prasad
1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / c aaron franklin del
1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / sheikh rashid
Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.
www.berquetechnologies.com
berquetechnologies@gmail.com
Is This Answer Correct ? | 9 Yes | 3 No |
How can we parallel two transformer with vector gorup YNd11 and YNd1?How is connection two transformer GT?
What is the formulae of Megger value for a A.C.Motor
what are the types of 3-ph. generator protection
How to calulate cable size for 200KVA,160KVA& 40KVA load?
what is the highest transmission voltage in India till now?
What is super thermal power plant? and how it will differ from normal thermal power plant
The slip during plugging operation is given by= A 1-s B 2+s C 1+s D 2-s
What is the high tension lines voltage and low tension lines voltage?33 kv is high tension line or low tension.
HAI SENT HPCL APTITUDE QUESTION PAPER, MY EMAIL ID IS angus_eee04@rediffmail.com,angus_eee04@yahoo.com
difference between converter and invertor
Two bulbs of 500w and 200w rated at 250 v will have resistance ratio as ?
2 Answers CGL, Dreamz Infra, Sunny Developers,
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?