why ht motor connection in star

Answers were Sorted based on User's Feedback



why ht motor connection in star..

Answer / avdhesh

HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.

Is This Answer Correct ?    86 Yes 1 No

why ht motor connection in star..

Answer / madhanc

Normally Motors starting current when using of DOL/Delta to avoid the starting current and insulation we are using Star delta connection to protect the motor from the insulation fails and reduce starting current

Is This Answer Correct ?    5 Yes 0 No

why ht motor connection in star..

Answer / shivaji chaudhari

for limiting starting current.

Is This Answer Correct ?    12 Yes 9 No

why ht motor connection in star..

Answer / anand

Ht motor star connection current is root 3 times low carried & power saving but delta connection current is high

Is This Answer Correct ?    0 Yes 0 No

why ht motor connection in star..

Answer / svrao

HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.

Is This Answer Correct ?    0 Yes 0 No

why ht motor connection in star..

Answer / narayanaswamy

I am of the opinion that star connection of HT motor is done to have better operation of protective gear

Is This Answer Correct ?    0 Yes 0 No

why ht motor connection in star..

Answer / kumar

because ht motor starting current always high so that
motor connection should be star to delta for limiting the
starting current.the principle is that staring position
motor connection in star later it change to delta

Is This Answer Correct ?    19 Yes 20 No

why ht motor connection in star..

Answer / pankaj gajare

Because HT motor having large starting current so that if
your connection will be in star then your current will be
root three so its automatically reduce.
its star delta principle...in star connection current will
root three times reduce.

Is This Answer Correct ?    3 Yes 10 No

why ht motor connection in star..

Answer / jameel

the ht motor connection in star because it is easy and
cheaper than delta connection in high voltage and star
delta connection not used in this system .
and the best question here why the ht capacitor of power
factor connection star not delta although the delta
connection is more economecal than star. we need in star
three times farad(reactive power) of ccapacitor than delta
but we connection star not delta because the same reason in
ht motor.
but the ht transformer some times it is necssary to
conection the primary or the secondary or both delta
accrding to the requirment of network.

Is This Answer Correct ?    2 Yes 9 No

why ht motor connection in star..

Answer / priti

in star connected sysytms...u can provide it with a
neutral..so that in case of faults the fault current will
flow through the neural nd hence preventing shocks!!

Is This Answer Correct ?    1 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

Difference between PLC and SCADA ? What are merits & De-merits of PLCs ? What are merits & De-merits of SCADAs ?

3 Answers   Ambuja,


what is the soft starter principle? how is connection diagram? what is the procedure for checking the connection?

0 Answers   Siemens,


what will happen if we directly give supply to rotor of a induction motor?

1 Answers  


why in 3.5 core means 3 core for phase and .5 for neutral?

1 Answers   Sodexo,


Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv

0 Answers   India Cements,






What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?

0 Answers   Hira Group,


Details about Flux Compensated magnetic Amplifer starter for motors

0 Answers  


int a,b ; a=b=10 ; if(a>b){ printf ("%d",a)}; no error output is a=10

2 Answers   TCS,


Block diagram of Power line communication?

0 Answers   CIL, VIP,


is it necessary to earth the rmu before cutting off the transformer winding?if yes why?

0 Answers  


what is electricity

4 Answers  


what current is taken from a double wound 500kva transformer

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)