why ht motor connection in star
Answers were Sorted based on User's Feedback
Answer / avdhesh
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
Is This Answer Correct ? | 86 Yes | 1 No |
Answer / anand
Ht motor star connection current is root 3 times low carried & power saving but delta connection current is high
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / svrao
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / narayanaswamy
I am of the opinion that star connection of HT motor is done to have better operation of protective gear
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pankaj gajare
Because HT motor having large starting current so that if
your connection will be in star then your current will be
root three so its automatically reduce.
its star delta principle...in star connection current will
root three times reduce.
Is This Answer Correct ? | 3 Yes | 10 No |
Answer / jameel
the ht motor connection in star because it is easy and
cheaper than delta connection in high voltage and star
delta connection not used in this system .
and the best question here why the ht capacitor of power
factor connection star not delta although the delta
connection is more economecal than star. we need in star
three times farad(reactive power) of ccapacitor than delta
but we connection star not delta because the same reason in
ht motor.
but the ht transformer some times it is necssary to
conection the primary or the secondary or both delta
accrding to the requirment of network.
Is This Answer Correct ? | 2 Yes | 9 No |
Answer / priti
in star connected sysytms...u can provide it with a
neutral..so that in case of faults the fault current will
flow through the neural nd hence preventing shocks!!
Is This Answer Correct ? | 1 Yes | 9 No |
Difference between PLC and SCADA ? What are merits & De-merits of PLCs ? What are merits & De-merits of SCADAs ?
what is the soft starter principle? how is connection diagram? what is the procedure for checking the connection?
what will happen if we directly give supply to rotor of a induction motor?
why in 3.5 core means 3 core for phase and .5 for neutral?
Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
Details about Flux Compensated magnetic Amplifer starter for motors
int a,b ; a=b=10 ; if(a>b){ printf ("%d",a)}; no error output is a=10
Block diagram of Power line communication?
is it necessary to earth the rmu before cutting off the transformer winding?if yes why?
what is electricity
what current is taken from a double wound 500kva transformer