Why HT motors are connected in star.
Answers were Sorted based on User's Feedback
Answer / pallamraju
in star line current =phase current
line voltage =1.732* Ph voltage.
if we connected in star there is no change of current parameter.insulation level can be minimized.hence size of the motor will be reduced.if in delta it will be more.that's why all HT motors ,syns motors & generators in star connected system.
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / gunasekaran
1.we can use less no of turns for same voltage level
2. we can put less insulation.
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / giri
Starting current is reduced 1/3 times during star connection
starting since voltage also reduced by the same proportion
.U can remind in star-delta connection starter.
Is This Answer Correct ? | 9 Yes | 8 No |
Answer / n. gopal krishna (hf)
In star line voltage =1.732*phase voltage &In delta
Vl=Vp.so we can not provide much insulation in delta
connection. we cannot use also differtional relay in delta.
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / s c budhiraja
To reduce starting current as well as avoiding star -Delta
starter, the motor stator is connected in Star.
Is This Answer Correct ? | 3 Yes | 4 No |
A CT is marked as 10VA 0.2FS in its name plate. What is it? Where it is used?
what is the criteria for selecting fuse rating in 1phase, 2phase & 3phase welding sets?
why wire sizes are 3/29 or 7/29 and why not wire sizes are 2/29 or 6/29?
The corona effect is more in a) summer b) winter c) dry weather d) humidity weather
What r the specification furnishid in motor name plate?
How to calculate KW what is the formula for KW.
what is the condition for YnD11
how to check the stabilty test for generator differential protection
What will happen if the rotor circuit of a slipring I.M. is kept open & electric supply is given to its stator winding.
Define peak overshoot.
what is the major difference between dc generator and synchronous generator?
when we change tha taps from 1-16 in 100mva tr whether a constant voltage avaliable till it reaches tap 16 or voltage change as per taps change