how tan-delta test is performed?
Answer / k.prakashchandra
HV Tr ratio arm bridge is used for measurement of tan delta
and capacitance.The tests are conducted with 1.HV winding vs
LV winding grounded to tank.2.LV vs HV grounded 3. HV vs LV
ungrounded.4.Bushing insulation with respect to test tap.
The highest is selected .Test voltage is 2.5 to 15 KV for HV
and 1 to 1.5 KV for LV, in case of 110/11 KV Tr
| Is This Answer Correct ? | 3 Yes | 4 No |
how to measure the voltage drop in cables also give formulas to calculate.
Why we are using LA Rating 10kA in 66 kv substation
differnce between single acting and double acting solenoid valves
How many types of DC current
How much duration I can keep open the CT if it is under loading condition(100 Amp load)?
3 Answers Infosys, NTPC, Suzlon,
why we are 0.8 power factor only?
for testing busbar (33kv) hi-pot .whether we can apply DC r not.and what is the test volt for that .explain
line tester lamp working in which voltage?
What are the types of transformers according to the arrangement of iron cores?
wat is d first thing to be seen 2 lay a cable in a particular area??
Define active and passive network?
How can i calculate the Breaking capacity of molded case circuit breaker, is the breaking capacity of CB for Diesel generator shall be less than grid supply's breaker ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)