Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why fuse not recomended to neutral

Answers were Sorted based on User's Feedback



why fuse not recomended to neutral..

Answer / sennapparajan

Neutral is return path of the circuit only. fuse is used to
protect equipments.so while over current or short circuit
circuit to be dicconnected before equipment. so in
neutral ..fuse is not recomended or not required.

Is This Answer Correct ?    54 Yes 17 No

why fuse not recomended to neutral..

Answer / gopal prasad

Fuse is an device used to protrct the wireing,in case of
over current,short circuit conditions.When this type of
fault occurs in a system or failure of insulation, maximum
fault current flows in wire.If fuse is connected to the
neutal:
(i) fuse will not blow when phase is shorting with
earth line and cause fire hazard.
(ii)if fuse is blown off then also phase supply
(live)will be available which wilb dangerace for the peson
thinking that no power is available to the equipment.

Is This Answer Correct ?    22 Yes 5 No

why fuse not recomended to neutral..

Answer / swadesh

Fuse is used for safety as well as the protection of the
equipment.When short circut occurs and if fuse is connected
to the neutral then fuse of neutral will be blown off, but
it is of no use because we are disconnecting the path that
is directly connected to the earth. Since our body is also
at ground and neutral is also grounded therefore if neutral
is not disconnected then it will not effect the safety,
because if someone touch the neutral(seperately} it will
not cause of shock wheather fuse is connected
Now if live supply is not disconnected it will cause shock
to the prson, since our live supply is not at ground
potential.
Therefore it is mendatory to connect fuse in live portion
and it is of no use to connect fuse in the neutral.Besides
of that during short circuit fault neutral will give return
path to the faulty current.

Is This Answer Correct ?    13 Yes 4 No

why fuse not recomended to neutral..

Answer / praveen

fuse is used to disconnect the circuit from supply under
fault condition . It will never use on neutral because when
the fuse blow under fault condition the phase wire will
still connected to the equipment and hence the person can
get shock how come in contact with the equipment.

Is This Answer Correct ?    7 Yes 1 No

why fuse not recomended to neutral..

Answer / baljinder singh

in three phase supply , if neutral is break for any reason
the two phase voltage came across equipment . so it damage
the the equipment ....

Is This Answer Correct ?    8 Yes 2 No

why fuse not recomended to neutral..

Answer / ashok mishra

Fuse is used for safety as well as the protection of the
equipment and operator too.fuse can b connect in neutral as well as in phase
the fuse will work as the same on both (in natural or in phase)
IER make this rule to connect the fuse to the phase only just to the safety of equipment & operator
and if there is a earthing and fuse is connected at the neutral and there is a inrush of current fuse will disconncet the neutral after disconnecting the nutral earthing will make itself as a return path and the equipment will damage altimeatly
and operator comes in contact with that equipment than due to the connection of phase he/she can suffer a shock
due to these both reasons fuse is connected in phase only
swami devi dyal

Is This Answer Correct ?    1 Yes 0 No

why fuse not recomended to neutral..

Answer / rob martin

I work in the medical electronics field. Sometimes fusing
both is a good idea and even recommended. Refer to this
article:
http://ewh.ieee.org/soc/pses/Downloads/newsletters/88v01n5.p
df.

Is This Answer Correct ?    5 Yes 6 No

why fuse not recomended to neutral..

Answer / gunasekaran

if fuse is blown unbalance is occurred so it will destroy
the equipment so link is recommended

Is This Answer Correct ?    2 Yes 7 No

why fuse not recomended to neutral..

Answer / anupreet

if fuse is connected to neutral,it will catch fire...and may damage equipments

Is This Answer Correct ?    0 Yes 15 No

why fuse not recomended to neutral..

Answer / nihar ranjan sahoo

Fuse is an equipment used to protrct the circuit,in case of
over current,short circuit conditions.When this type of
fault occurs in a system, maximum fault current flows in
phase wire.so only in phase wire FUSE is connected.

Is This Answer Correct ?    12 Yes 28 No

Post New Answer

More Electrical Engineering Interview Questions

how to find Harmonics and types as per the equipemnts

0 Answers  


What are IR values and what it should be for coil and for insulator

0 Answers   GPSC Gujarat Public Service Commission,


Why it is possible to use PWM with a STATCOM and not with a conventional TCR based SVC

0 Answers  


We know that primary transmission is done to reduce current so that i^2*r loss could be minimised but according to ohm's law v is directly proportional to i,which indirectly means higher potential difference means larger current?so how the current is minimised in high power transmission line??

2 Answers  


I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A

4 Answers  


How to find the maximum load, that can be supplied by a transformer.....

2 Answers   ME,


A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.

0 Answers   Jindal,


Where all & Why resistance grounding is required?

1 Answers  


who & how the notations given as RYB to 3phase power supply.

1 Answers  


What is the out put of a CT? How the ratio is decided ?

1 Answers  


what is the differences between microprocessor and general purpose computer

0 Answers   Stesalit,


How does an induction motor start?

0 Answers   Ericsson,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)