What is the difference between AMF panel and DG
Synchronization panel? please define the working of both
the panels?
Answers were Sorted based on User's Feedback
AMF Panel: is Auto Mains failure panel. When the EB power
goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization, there is no outage of supply to the
utilities.When the incoming genset is to synchrinize with
the existing set,we've to match the magnitude of the
voltage, phase angle and the frequency and then only we've
to switch on the incoming set's breaker.
Is This Answer Correct ? | 85 Yes | 10 No |
Answer / bhupinder singh verma
AMF Panel: is Auto Mains failure panel. When the EB power goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization OF DG SETS, When the EB power goes off with a time delay signal will go to DG self starter to start the DG AND WHEN THE LOAD REACH THE 90% CAPACITY OF THE DG-1 THEN THE DG-2 WILL START AND THE DG-2 gen-set is to synchronize with the existing DG-1 THEN ,we've to match the magnitude of the voltage, phase angle and the frequency and then only we've to switch on the incoming set's breaker. THATS WHY THE OUT PUT SUPPLY SUPPLY OF BOTH DG SET WILL RUN ON THE SAME COMMON BUS BARS ( MEANS- DG-5OO KVA / DG-2 380 KVA THEN THE TOTAL LOAD IS 780 KVA ON COMMON BUS BARS ) IN THIS WAY WE CAN SYN. ELECTRICAL CITY BOARD POWER AND DG POWER ALSO.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ajith kumar.s
1 st answer is right
but synchronization of palel is deffernt types one is rpm
synchronizing other is voltage and phase sequency this
uesed dark lamp or synchrocape used,
Is This Answer Correct ? | 11 Yes | 13 No |
what is the difference between circular wdg & ractangular wdg?
make control wire diagram of start and stop a function with a single push button
What current flows in the transformer primary when its secondary is open?
for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
explain supply side and demand side energy management with advantages & disadvantages
TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?
What is Load sharing of Transformer ?
Equal resistance of 100ohm each are connected to the arms of whestons bridge, which is supplied by 2v battery. The galvanometer can sense a current low as 1microAmp. What is the smallest resistance that can be measered.
Percentage losses in power generation?
Do you have any P.L.C in your organization?
What is current divider rule (cdr)?