what is the procedure to carry out BDV test of a
transformer ?
Answers were Sorted based on User's Feedback
Answer / p.s.suresh
1. first we will take filltered oil in test kit.
2. then maintained 2.5mm gap between electrode and applying
rated 40 & 60 Kv for 1 minite .
3. the above test withstood for 1 minite its ok for
energiseing the transformer.
Is This Answer Correct ? | 22 Yes | 9 No |
Answer / c.b.sharma
1.first we will take filltered oil in test kit.
2. then maintained 2.5mm gap between electrode and applying
rated 40 & 60 Kv for 1 minite .
3. the above test withstood for 1 minite its ok for
energiseing the transformer.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / vinod
1)Take transformer oil sample from both bottom and top
section with suitable container on dry day
2)Adjust the BDV kit electrode for 2.5 mm and ceck with
gauge, increase the voltage till breakdown occur
3)Now a day automatic tester is available it will take
consicutive five readings with stiror. third reading will
be the BDV.
Is This Answer Correct ? | 8 Yes | 3 No |
what is the difference betwteen overcurrent and short circuit fault?
what will happen to give a dc supply in transformers?
from which formula we select a capacitor rating?
what r the safety measures in UPS ? explain all?
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
What are the operation carried out in thermal power station?
WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?
Hello to all, Please someone can send me HPCL ELECTRICAL Engg. Sample papers to me? Its urjent....my email address is.... raviasiapacific@gmail.com
Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
Expand sqcm?
What will be the capacity of the generator set which can be used for my 2 ton window air conditioner ?
Differentiate between magnetic field and magnetic flux?