Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What will be the full load current of 60KVA UPS. Suggest
for this formula.

Answers were Sorted based on User's Feedback



What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sujit288

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    71 Yes 8 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / muralidhar k.s

Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva

Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.

Is This Answer Correct ?    23 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sreenu

Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.

So I(Current)= S (Apperent power)/Voltage only.

Is This Answer Correct ?    5 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / guru

i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....

Is This Answer Correct ?    3 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / murugesh.k

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    4 Yes 2 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sathishbabu t

p=v*i*cos

Is This Answer Correct ?    3 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / rahul

Full load current =Kva*1000 /v*Powe factor

Is This Answer Correct ?    0 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / kumar

formula of 3 phase power calculation

p=1.732*VL*IL*cos@

60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS

Is This Answer Correct ?    9 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

if an induction motor is operated at unity power factor what will happen? will motor run or not? kindly describe a logical answer?

2 Answers  


What is the difference between a Vacuum Circuit Breaker and a Load Break Switch?

7 Answers  


What is the difference between PLC and Embeded system

0 Answers  


why dc is used in control circuit for mv & hv switchgear instead of ac

0 Answers  


How to Select transformer for 100HP motor plz... With calculation

2 Answers   Rasandik,


what is the relation between the size of the machine and the frequency? (when the frequency increases the size of machine will increase,why?)

2 Answers  


why is efficiency of transformer more than that of other rotating machines?

1 Answers  


state application of relay in transmission line?

4 Answers  


WE HAVE A LOAD OF 55KW MOTOR ITS VOLTS 380 3PH AND ITS TAKING 100AMPS (ITS FULL LOAD IS 105AMPS)AND ITS CABLE IS 4CX50SQMM ,NOW ITS GETTING ABNORMAL HEATUP IN CABLE,PLZ TELL WHY ITS HEAT-UP?(CABLE LENGTH IS 15 METERS ONLY)

10 Answers  


Explain why machinery used on a.c supply is usually rated in KVA instead of KW?

10 Answers   EEE, Mtandt,


we use 400/5A ct and 35/roor3KV,/0.1/root3KV,0.1/root3KV pt ratio. What is the multiple factor of this meter.

0 Answers   ABB,


What are the common sources of energy?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)