What is the effect of leading power factor for power
transformer & D.G?
Answers were Sorted based on User's Feedback
Answer / rabi
The stability of a generator depends on the field strength
of the magnetic field establishing in the air gap by the
rotor ampere turn. if the field is weakened the stability
margin is reduced.
Leading power factor causes field mmf (fm) to reduce and
rotor angle to increase towards 90 degree, the theoretical
operation of stable generation operation. Therefore a
machine operates well within its stability limit factor
with lagging power factor.
Transformer operation does not depend on power factor. For
that reason it is rated in KVA.
| Is This Answer Correct ? | 25 Yes | 6 No |
Leading power factor makes the current leading the voltage
it does not affect the transofmer but it affects the
D.G./Power generation unit. As for the power generation we
need to excite the excitor field which take the sensing
reference voltage from the output line of the generator.In
case of leading power factor the voltage will not dip on
increasing the load and hence the AVR will not be able to
excite the system properly.
| Is This Answer Correct ? | 20 Yes | 4 No |
Answer / deepak chander
The transformer opration does not depends on the pf. The
major problem in leading pf is related to generation.
Stator end region heating depends on the pf. In leading pf
the altenator run at underexited operation and there is the
scope for flux to increase even over the saturation limit
of core. That causes the core heating on end region.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ramesh kumar gupta
Leading power factor does affect the power Xmer within its
VA rating but it affects the D.G./a Generator unit.Due to
leading power factor the source excitation system runs in
under excited state and the deficit in excitation has to be
supplied by stator.Owing to this stator end core heating
problem observed.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / suresh
Leading power factor, means making Cos factor nearer to 1,
hence doing so you can achive the following,
1.partial reduction in load current hence losess get reduced
2.Efficency increases
| Is This Answer Correct ? | 5 Yes | 13 No |
Answer / guest
Leading power factor causes the the current to reduce,due to
which the generator gets overloaded at its full load capacity.
| Is This Answer Correct ? | 5 Yes | 34 No |
what about SAP/MRP regarding manufacturing of electric motors and all drives?
what is the purpose of high speed earth switch in gas insulated substat
WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off 10kv 20kv 30kv
which protection function should measure RMS value of current&DFT value of current?
What is the comparison between 30mA DP RCCB and 100mA DP RCCB and can replace it against 63A MCB
how do you reduce the skin effect
how to calculate unit consumption on 3phase 380-415 v0lt kilowatt motor eg ( 55kw,380v,3phase 50-60hz)
What are diffrent type of road taxes?
why the Parameters : Base Voltage & Maximum Voltage can't be equal in value in a VFD (Variable Frequency Drive) ? How much the base voltage would be lower than the maximum voltage ? If 400 V is the 3 phase output of a VFD ... then what should be the base voltage ? thanks a lot
What_is_mean_by_negative_dc_voltage? why we use -48v except +48v in DC power supply systems.
What is a Single Phase and Three phase Power? How it will be converted or transformed into another form?
What is erection of electrical system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)