What are the different pre-commissioning tests that are
performed on the distribution transformer, power cable and
switchgear (11kv)?
Answer / pillay
Most importantly the insulation and HV holding test is done on
all the installations.
on the tx former;winding insulation test,
ratio test, vector group test,impedence test, oil dielectric and
other test,
bucholtz relay test, all protective equipments operation test,the
switchgears insulation and conductivity tests along with pressure
tests on cables also . all tests have to meet the local
requirements or as relevant BS.
| Is This Answer Correct ? | 15 Yes | 3 No |
How to power regulated by AVR in Alternator?
what is different between IP55,IP54 and IP66?
2 Answers ABB, Global Industries,
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
in small capacitor we use uf( micro farad) and in big quantity we used kvar. i want to know that in 1 kva how much will b uf(micru farad).
If single phase voltage level is 230V than why three phase voltage level is not 660V ?, but it is only 440V.
16 Answers BSNL, DOS, EFS, HMT, L&T, TCS, ThyssenKrupp,
Explain the working principle of Vacuum circuit breaker and Air circuit breaker
10 Answers HP, Trinidad and Tobago Electricity Commission T TEC,
What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.
WHY THE COLOUR OF TRANSFORMER IS GREY ?
sir, 3phase induction motor takes different pf and different KW in three phase while running,explain reason
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
WHAT WILL HAPPEN WHEN THE MOTOR FREQUENCY INCREASED OVER THE RATED MOTOR RPM THROUGH DRIVE?
How to select a D.G set for calculated load of 110kW..?
7 Answers Shakthi Power Systems,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)