Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to callibrate a new i/p converter

Answers were Sorted based on User's Feedback



how to callibrate a new i/p converter..

Answer / binu

Connect the input air suply of around 5 to 7 Barg. Feed 4
mA through the calibrator, the output aire pressure gauge
shal indicate 3 psi. Feed 20mA through the calibrator, the
output air pressure gauge shall indicate 15 psi.

Is This Answer Correct ?    25 Yes 4 No

how to callibrate a new i/p converter..

Answer / guest

hi sanjay
1. AIR SUPPLY
I/P input - 1.4kg/cm2
Out put - 0.2 to 1kg/cm2 ok

2.input signal= 4-20 mA

i.connect the air supply to input with the hepl of REGULATOR i.e 1.4kg/cm2
ii.connect the MASTER GAUGE to OUT PUT ok

Apply the signal

i. 4mA- 0 kg/cm2 (if not Zero/0.2kg/cm2 Adjust Zero adjustment Screw)
ii. 20mA-1 kg/Cm2 (if not 1kg/cm2 Adjust Span adjustment Screw) ok.

then 8, 12, 16mA.
min. and max. is ok the remaining will perfect automatically i.e 8,12,16mA.

and MAIN IMP POINT is ON the I/P's Ckt board Side 4 adjust ment buttons is there and adjust that buttons Direct and Revese Actions ok

Is This Answer Correct ?    20 Yes 0 No

how to callibrate a new i/p converter..

Answer / asif javaid

FIRST SEE ITS PRESSURE RANGE APPLY INPUT PRESSUR 5PSI
MORE THEN MAXIMUM RANGE OF OUTPUT PRESSURE AND SEE ITS OUT
PUT THEN APPLY 4MA AND SEE OUTPUT SIGNAL 3 PSI NOW ADJUST
3 PSI FROM ZERO ADJUSTMENT SCREW NOW 8 12 16 &
20MAAPLY AND CHECK MAX PRESSURE RANGE NOW ADJUST FROM SPAN
SCREW

( RANGE CAN BE DIFFERENT FROM 3 TO 15 PSI )

Is This Answer Correct ?    7 Yes 0 No

how to callibrate a new i/p converter..

Answer / haridass

Friends, plz understand the question first. The
interviewers has mentioned "how to calibrate a NEW i/p
converter?"
Why the new i/p needs calibration?

Your answer must be like this..

"Sir, the new i/p would be factory calibrated with high
accuracy master instruments, so before we commission it in
the plant we have can check its output by applying proper
signal, unless we have good accuracy masters we no need to
disturb the calibration. If yes, we can do the calibration
using the 30psi regulated supply, 4-20 mA source, and
receiver gauge."

Is This Answer Correct ?    8 Yes 1 No

how to callibrate a new i/p converter..

Answer / charlie daubitz

There can be a jumpper on the I-p converter to set the
range. There are more accepted ranges than only 3-15 psi.

Is This Answer Correct ?    4 Yes 0 No

how to callibrate a new i/p converter..

Answer / binu

Dear Sanjay,

Hope you are adjusting 4mA with "Zero" screw and 20mA
with "Span/range" screw. I feel that you might have
adjusted the 3 psi with range screw.

Is This Answer Correct ?    0 Yes 2 No

how to callibrate a new i/p converter..

Answer / sanjaymaven

i follow your above procedure
i use 0-30 psi pressure gauge
when i feed 4 mA gauge show 3 psi, gradually i increase mA
, simontaneously pressure increase.At 10 mA gauge shows maxm
20 psi. i little adjust the range screw but nochange on
gauge. now what will i do .please sujest

Is This Answer Correct ?    3 Yes 9 No

Post New Answer

More Instrumentation Interview Questions

Hi i m B.E. In elect. & comm. I m workin in bio mass plant from 6 mnths as inst. Engg. but now i m in dept. Of operation as shift engg...which is best operation or inst. 4 me? M confusd..plz help and reply me..

2 Answers  


why to use 3 wire at RTD ? what's the reason for common wire ?

4 Answers  


what is difference between venturi and orifice

1 Answers  


can anyone tell free downloads website for fundamentals and principle of basic pressur,temperature,level and flow

2 Answers  


How to change dcs card in online. (Dsc is maxdna)

3 Answers  


What are the different modes of a contollogix family processor? How they work?

3 Answers   Honeywell, Siemens,


What is rtd output signal

4 Answers   Nestle,


what is concept of field,control room area in transmitters?

1 Answers  


In power plant to measure vibration of a turbine we install sensors. Before install this sensor we have to set gap voltage. What is meant by gap voltage and its use?

0 Answers  


Please explain about FAT? What is the difference between FAT and SAT?

6 Answers   IBM,


why we use the ac supply load cell>?can we use the dc supply load cell?advantages and disadvantage of the ac supply load cell?

0 Answers  


Define all the process Variable and state their unit of measurement. ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)