THE 40 MW OF POWER FOR 220 V III PHASE POWER CONNECTION
REQUIRES HOW MANY KVA POWEER REQUIREMENTS
Answers were Sorted based on User's Feedback
Answer / reshi
If we assume the power factor during motor running as 0.85.
Then the calculation will be 40MW/0.85= 47MVA.Answer.
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / riyadh
this formula u going to apply
Kw=Kva*P.f
we know P.f = 0.9 for T/f's
P.f = 0.8 for Generator
we knw power kw 40Mw
Apply to above formula Kva = kw / p.f
Kva = 40000 Kw / 0.8
Kva = 50000 kva
In Mva is 50
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / chethan
p- 40MW,v,220volts kva=?
40*1000000*4.54Amps multiply (1000=1.732*220*I,ans.4.54)
Ans. 181600 KVA
this is my knoldge ,so this is error,please tell me the
correct answer.
Is This Answer Correct ? | 0 Yes | 0 No |
Its 50000Kva on .8 pf and answer#3 is correct.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jayaraj
The question is wrong. 40MW load could not be fed from 220v 3 ph system. If the question is the KVA requirement 50000KVA on .8 pf. So in a distribution system 2000KVA Transformer 25 nos are required.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / v.s.narayanaswami
THE ABOVE FORMLA APPLIES FOR CONVERSION OF HP INTO KVA AND
THE CORRECT CONVERSION FACTOR IS 0.764.
THE REQUIREMENTS OF 40 HP CONNECTION CONVERTED INTO KVA
APPLYING THE FORMULA IE 1 HP = 0.764 KVA IS 40HP/0.764 IS
APPROXIMATELY IS 52 KVA.
HENCE UR CORRECT REPLY IS SOLICITED FOR ARRIVING AT THE KVA
DEMAND FOR THE ESTIMATED 40 MW OF POWER CONNECTION
REGARDS
V.S.NARAYANASWAMI
B.COM(HONS), M.COM, F.C.A
Is This Answer Correct ? | 2 Yes | 12 No |
Your B.tech marks is being given in CGPA grade. How is it calculated?
when the diameter of the core and cable is doubled, the value of capacitance ?
Triping principle of ELCB&RCCB? wht is the difference between these two?
Define motor & pump?
How many devices can be connected in one zone of FACP
What is restricted earth fault protection ?
WHAT HAPPEN WHEN A DROP OF WATER MIXED UP WITH TRANSFORMER OIL ?
what is the condition for vector group of Dyn5
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
Compare salient pole and Hndrical rotor machines.
what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)
12 Answers Afcons, Bhel, CIHSR, DCS, IOCL, L&T, Lupin, Siemens,
what is meant by frequency ?