What is the formula for calculating Transformer Losses &
Efficiency. I want to compare the Transformer efficiency at
different loading condition.
Answers were Sorted based on User's Feedback
Answer / kashifhabib
Efficiency = (Output/Input)*100
&
Output (KW)= KVA * Power Factor
Input = Output + Iron losses + Copper losses
Iron losses are due to Primary voltage so remains constant
can be calculated by open circuit test
Copper losses are due to secondary current I*I*R
can be calculated by short circuit test
Exp: Full load copper losses 800 W
1/2 load copper losses will be 200 watts
| Is This Answer Correct ? | 368 Yes | 101 No |
Answer / vinod parasa
Efficiency = (Output/Input)*100
output=(x)(KVA * Power Factor)
input=(x)(KVA * Power Factor)+(X)^2 copperlosses+core losses
the volue of x depend on load
x=1 for full load
x=0.75 for (3/4)th load
x=0.5 for half load
x=0.25 for quarter load
copper losses are variable losses and iron losses are
constant losses.
at the time of full load copperlosses=iron losse
Full load copper losses 800 W
half load copper losses=(X)^2 copperlosses
x=0.5 for half load
=(0.5)^2 *400
=0.25*400
half load copper losses=200
| Is This Answer Correct ? | 190 Yes | 85 No |
Answer / n.makali
POWER Transformer is 55MVA, 27/11.5KV ,efficiency =99.49
Find the Losses of Transformer
| Is This Answer Correct ? | 89 Yes | 35 No |
Answer / s.ravi
Efficiency =
(Output/Output+Iron losses+Copper losses)*100
Iron losses = No load test,
Copper losses = Short circuit test
Regulation = (Impedance voltage/Rated input voltage)*100
Impedance voltage = Short circuit test(Voltage drop)
| Is This Answer Correct ? | 59 Yes | 33 No |
Answer / prof dr lehaz kakakhel
go for two tests
open and short circuits tests
From the open, u compute the core power loss and from the
short, u get copper losses. then the formula is
efficiency = output/ (output + the above two losses)
SIMPLE
| Is This Answer Correct ? | 36 Yes | 19 No |
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
cany anyone suggest electrical wesites for providing study materials?
A 50Hz,4-pole,3-phase,star-connected synchronous motor has a synchronous reactance of 12ohmsper phase and negligible armature resistances.the excitation is such as to give an open-circuit voltage of 13.2kilovolt.the motor is connected to 115kilovolt, 50hertz supplying. what maximum load can be the motor torque,line current and power factor?
how to carried out tan delta test in 11 KV alternator ?
Why the transformers are rated in kva?
11 Answers Birla, NTPC, Reddy Labs, Vijai Electricals,
how to convert 1 phase power to 3phase power by using induction motor. . . .
WHAT IS EDDY CURRENT LOSSES AND SKIN EFFECT LOSSES IN ELECTRICAL ENGINEERING
Why Water motor is not taking a load or pressure while everything is correct. (Note: Motor running properly)
why ohms law does not obey semi-conducters?
How to calculate cable size in sq units based on motor rating is KW
if we going for high voltage usages what are the considering factors, why those factors are effected.... please give me an answer related motor factors like wnidnig, frame, temp etc
What is the formula to find out cross sectional area of cable for certain current rating?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)