What is the formula for calculating Transformer Losses &
Efficiency. I want to compare the Transformer efficiency at
different loading condition.
Answers were Sorted based on User's Feedback
Answer / kashifhabib
Efficiency = (Output/Input)*100
&
Output (KW)= KVA * Power Factor
Input = Output + Iron losses + Copper losses
Iron losses are due to Primary voltage so remains constant
can be calculated by open circuit test
Copper losses are due to secondary current I*I*R
can be calculated by short circuit test
Exp: Full load copper losses 800 W
1/2 load copper losses will be 200 watts
Is This Answer Correct ? | 368 Yes | 101 No |
Answer / vinod parasa
Efficiency = (Output/Input)*100
output=(x)(KVA * Power Factor)
input=(x)(KVA * Power Factor)+(X)^2 copperlosses+core losses
the volue of x depend on load
x=1 for full load
x=0.75 for (3/4)th load
x=0.5 for half load
x=0.25 for quarter load
copper losses are variable losses and iron losses are
constant losses.
at the time of full load copperlosses=iron losse
Full load copper losses 800 W
half load copper losses=(X)^2 copperlosses
x=0.5 for half load
=(0.5)^2 *400
=0.25*400
half load copper losses=200
Is This Answer Correct ? | 190 Yes | 85 No |
Answer / n.makali
POWER Transformer is 55MVA, 27/11.5KV ,efficiency =99.49
Find the Losses of Transformer
Is This Answer Correct ? | 89 Yes | 35 No |
Answer / s.ravi
Efficiency =
(Output/Output+Iron losses+Copper losses)*100
Iron losses = No load test,
Copper losses = Short circuit test
Regulation = (Impedance voltage/Rated input voltage)*100
Impedance voltage = Short circuit test(Voltage drop)
Is This Answer Correct ? | 59 Yes | 33 No |
Answer / prof dr lehaz kakakhel
go for two tests
open and short circuits tests
From the open, u compute the core power loss and from the
short, u get copper losses. then the formula is
efficiency = output/ (output + the above two losses)
SIMPLE
Is This Answer Correct ? | 36 Yes | 19 No |
hi everybody how to design string combiner box (scb) internal parameters like bus bar and spd (surge protection device and fuse which place to set that,and also bus bar one particular cross sectional how much heat generated and how much power loss tell me Clearly and briefly
what is isolation Transformer?
Advantages of using bundled conductors ?
why Power transmssion voltages are as 11kV,33kV,66kV,220kV and so on only?
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?
why not starting switch first connect in direct on line starter?????
what is the diff. btwn. electronic regulator and ordinary rheostat regulator for fans?
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
why generator is design for lagging P.F(power factor)?
if voltage is not builed up in small generator what will be the reason?
What types domain of laplace transforms? What behavior can laplace transform predict how the system work?