How Calculat the Cable Sizing of HT/LT System & Explian by
one Exampal?
Answer / habib
Cable size (sq.mm.) is selected dpendent on 4 facors
1. Current carrying capacity (popularly termed Amapcity)
of the cable.
2. Voltage drop that can be tolerated at the load point.
3. Short circuit tolerance of the cable.
4. Mechanical strength of the cable.
A cable is selected fo the job that can meet all these
criteria.
Basically HT and LT cables are of same material but the
difference is in insulation.
Looks too much like a text book lesson. If you can post
your exact requirement, I would try to help.
Is This Answer Correct ? | 4 Yes | 2 No |
What is the minimum distance between taransformer (say 2000 kva)and its earth pit?
HOW CIRCUIT BREAKER RATING CALCULATED?WHAT ARE THE PARAMETERS CONSIDERED?
Assume a condition such that two motors of rating 6.6kv,415v are connected to blower,so tell me which motor draw large current give appropriate reason?
what will be fault level of 11 KV , 2000 A ELECTRICAL SYSTEM?
ful form of gis
What is the basic rule for block diagram reduction technique?
Compare salient pole and cylindrical rotor machines.
What's an AVR? What's its purpose in Generators?
what is the meaning of transformer short circuit test?
what are effects of harmonics in the three phase a.c power system ?
what are the highly demanded courses for electrical engg. who finished his b.tech
how to combine two linear transformers...............