a voltmeter shows 100v..wat is to be done to make it read 150v.
Answers were Sorted based on User's Feedback
Answer / madhusudhana
To increase Ammeter range, we add shunts and to increase voltmeter range, series resistance is connected to it. The device is calibrated accordingly.
Is This Answer Correct ? | 17 Yes | 0 No |
Answer / praful nandankar
Resistor is added in series to increase the voltmeter range.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / tinku
if you want to make the deflection of voltmeter on 150 volt
on appling 100 V you can reduce the series resistance of
voltmeter it will cause more current to folw through it and
will show more (false) reading. But if you actually want to
increase its range to 150 volt i.e. it can measure upto 150
V you have to increase the series resistance
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / latha
increase the number of turns in the pressure coil
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / manoj sharma
Ther are following solutions.
1. increase the souce voltage up to 150V, which is being
measured by voltmeter.
2. volt meter measure the voltage by a niddle which is
clibrated to show difflection acording to magnetic force
develored in the potential coil. So increase the number of
turns up to 1.5 times of present no. of turns.
3. Replace the potential coil with new coil having
inductance 1.5 times of present potential coil.
Any way but why you want to do so.....plz tell me geetha...
Is This Answer Correct ? | 0 Yes | 3 No |
Reversal of corrent feature in MCCB- What is reversalof current -explain broadly.
the distance from my office to d.g is aprox 400mtrs and voltage drops ibn my office near about 40 volt what should i do p[ls suggest.
Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
what is the effect of back reactive power on the generator ?
Do you know the overhauling of a motor?
how to maintain frenquncy with syncronising sub-station for distribution
how capacitor can split the phase.
How to connect the earthing in aircraft?
What are the types of windings present in the ceiling fan? What winding will be effective first when we started the fan?What are the resistance and inductance ratios comparatively at the initial speed and full speed of the fan?
high voltage transformer input voltage,current and amps rating..distributed transformer input voltage,current and amps rating...
WHY DG are rated in KVA or MVA ???., but ALL power plants are rated in KW or MW.,,?
How to select AC3 duty contactor for DOL & Star-Delta starters