how calculation to be done of cable size/o.h. conductor
size of 11kv h.t.for the load of 2175 kw
Answer / k.prakashchandra
The current is about 120 A. But it is not continuous.You
have to the study the list of OH conductors available in the
market.For 120 A and 50' Temp rise ,weasel ' ACSR conductor
is enough. Then you have to consider voltage regulation
which should not exceed 6% and further development. Rabbit
ACSR conductor is the next one with carrying capacity of 148
A for 30' temp rise and 183 A for 50 ' temp rise.Temp rise
is for calculation of maximum sag.
Is This Answer Correct ? | 1 Yes | 0 No |
how rating of transformer is selected for any new plant/what kind of load is cosidered/what kind of fadtors are considered/ pz give standard procedure
why for transformer protection we protect tranformer from 3rd hormonics and 5th hormonics and what is the reason of generating these horminics in electrical system?
if an alternator or turbine using fuel to produce ele energy and we didn't connect load to the ends then where was gone the ele energy
What is function for Load Bank test and why need to test.
What is the purpose of reactor in over head transmission line.Can you any explain it.
2 Answers Dr Reddys, L&T, Reddy Labs,
Can we manually synchronize two DG sets of same ratings manually without using speed biasing ? If yes then how?
why rating of motor in HP ?
What are the applications that use Solid State Drives in your home?
how to check IR values in alternator winding?
What are the main parts of VCB?
what is the procedure for cable sizing or on what basis we will calculate the size of cable?????
A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.