what is the function of buchhos rely in transformer
Answers were Sorted based on User's Feedback
Answer / ilononurb
Buchholz is a gas actuated relay which response if there is
any abnormality inside the transformer. Ex. If there a
incipient fault happens in transformer winding. arc causes
decomposition of oil that contains more hydrogen gas which
being light rise upward to bocholz relay. The gas is
collected to upper side of the relay. therby oil level drop
down in the B-relay that tilt the mercury switch that close
the alarm circuit.B-relay gives an alarm so that the
transformer can be disconected before the incipient fault
grows in to serious one.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / prashant
when there is any abnormal condition like
overloading,overcurrent,or any such things which increase
the tempreture of oil,,,then there will be gas bubble in
oil,,,,buchhos relay senses this abnormal condition,,,,
it will also give alarm signal if oil level is lower than
pre decide value,,,,,,,,,
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / kjh
I agree with answer #2 .I want to add some, B-relay has two
stages one is connected in alarm circuit and the other is
connected wtih tripping circuit.It also tripping the
incomming C.B. of the transformer in case sewear fault.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / atti
Actually Ans # 04 option # B IS not the function of b-Rely.The
function of B-REly is the smoke detection not to check the
leakage.Allthough It has a oil leve detector .
Is This Answer Correct ? | 0 Yes | 0 No |
It is known as BUCHHOLZ relay.
A buchholz relay is operated by the accumulation of air bubbles within a transformer.
a) When a short circuit happens within the windings or within the contacts of the tap changer or any other shortings a localised heating takes place and gasses are liberated within the transformer.
b) When there is a leak in the transformer and the oil level drops or
c) The temp drops too low and the oil level falls below the required level.
These conditions trigger the float switch within the buchholz relay. The contacts are used for tripping the transformer or to on an alarm.
Is This Answer Correct ? | 0 Yes | 2 No |
How do we calculate the resistance per metre of single core aluminium stranded cable 19*3.25mm sheathed in pvc,at 15 deg C temperature?
Please provide me detail cable voltage drop calculation
What is maximum rating of transformer ?
What can you contribute to the progress of our Company as an employee if you are selected?
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
hello... i am preparing for GET. please send me previous papers..
which course is maximum demand in industry and give me the list of best courses for electrical engineers
why do we generate only 3ph ac?is it possible to generate 4ph,5ph,....?
6 Answers Accenture, Bhel, Reliance,
why the starting current of a motor is high?
What is the normal earth resistance?
What’s electric traction?
Why transformer rating is represent in KVA?
7 Answers Bhel, Sonalika, Usha Martin, Wipro,