why it is important to earth neutral of 3 phase transformer?
Answers were Sorted based on User's Feedback
Answer / er. ankush miglani 9718151073
it is done to make the neutral at zero potential
coz if there is unbalance in potential the neutral may
shift.
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / guest
when there is a unbalace among the phases due to change in
load circulating current introduced this fault caurrent can
be eathed via neutral .
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / pranjal.job
it is because to make path for the current generated due to imbalance in d three phases
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / srinivas@vsp
for stepdown distribution transformers the secondery side ie
lt side y-with nutrel earhto be connected because of load
side the current is not zero ie varying.hence we r connected
y-with nutrel earh......... finally this because of stand by
earth fault in load sideie secondery side..
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / guest
to provide the protection from the over current,over loading
Is This Answer Correct ? | 0 Yes | 5 No |
What are unstable systems?
how to select the surge suppresor for the 33 KV supply and what will be the rating, selection guide
what is the condition for YnD11
What is the source of dependent source ?
difference between microprocesser and microcontroler
why neutral busbar size is half of the phase busbar size in control panels
what is the reason for earthing static equipments? why?
How to Make relay co ordination chart for a Electrical power distribution of a plant
How to calculate the current in DG What are the type of power pls explain with related formulas
1 Answers Corona Enterprises, Sodexo,
A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram
Is there is any hazard to insulation of 3hp motor 5 KV megger is used for it?
what is megar healthy value for ht < cables