what are the types used for alternator earthing,what will
happen if more than two alternator is working in
parallel with each having own system earthing.is there any
possibility for circulating current in between two system.
Answers were Sorted based on User's Feedback
Answer / prw
The earths of each alternator must not be connected at the
same time because this will result in third harmonic
current flowing causing excessive heating. The earth should
be switched so that only one earth is connected to ground
Is This Answer Correct ? | 17 Yes | 1 No |
if two alternators running parallel and both alternators
neutral grounded by one earthing strip, there is chance of
circulating current. because the unbalanced current flow
through the neutral of one alt.to second alt.by the neutral.
if both alternators earthing is separate , then no chance
of circulating current.
Is This Answer Correct ? | 13 Yes | 6 No |
the two types of earthing is used: 1. pipe type earthing
2. sheet type earthing
NOTHING WILL HAPPEN WHEN TWO ALTERNATORS ARE WORKING
PARALLEL WITH EACH HAVING ITS OWN EARTHING.
NO THERES NO POSIBILITY OF CURRENT CIRCULATION.
Is This Answer Correct ? | 7 Yes | 12 No |
How to improve the power factor from 0.8 to 0.98? Also tell me cost vs benefit analysis.
what is difference between armoured cable and un armoured cable
what is the difference between ac and dc?which one is more efficient?and what r their advantages
Give details on how you intend to handle a challenging position you are posted to manage unexpectedly as a company staff?
what are the advantages by using IGBT in VSC HVDC than thyristor in conventional HVDC
what do you mean by cl PS CTs? What are technical details required for it's manufacturing?
power transmission pole used one support , that only for support or earthing
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
Do Phase angle measurement have any application in freq/harmonics measurement? If so how?
could anybody able 2 send me jindal steels previous papers fr electrical steam....pls send 2 my id if possible....sirisha.shaik@gmail.com
3 phase supply is there Total kw 100 howmuch cable put the load
In legging current reactive power is arise but in leading current which power will be arise ? and in this case, is active power more than rated ?