New istallation how many eathing have one transformer?
Names of earthing connect places?
Answers were Sorted based on User's Feedback
Answer / makpsingh
Any transformer should have atleat four earthings.
2 connections for its neutral earthing and
2 connections for its body earhtings
All the connections should be with dedicated earth pits
which may be interconnected for relaiblity and to have
lower earth reistance value.
These earth pits should be duly marked and to be tested on
a dry day once in year of earth reisistance and earth
continuity. Earth Resistance value should be less than 5
ohms and if it is greater then these earth pits should be
treated to bring dowun the value.
| Is This Answer Correct ? | 61 Yes | 4 No |
Answer / vijay sagar reddy
Any electrical parameters have 2 Earthins
: 2 Neutral Earthing
: 2 Body Earthing
| Is This Answer Correct ? | 30 Yes | 0 No |
Answer / vijay sagar reddy
Any electrical parameters have 4 Earthins
: 2 Neutral Earthing
: 2 Body Earthing
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / gaurav sinha
Any transformer should have atleat four earthings.
2 neutral earthing and
2 body earhtings
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / manikandan
Thats depends upon the vector group of the transformer.in
case star-star,the neutral earthing is require 4Nos
(Primary/Secondary)earthing and transformer body is
required 2Nos earthing.Types of earting is more than 2.That
is depends upon the standard practice.
Types
1.Direct earthing(In India)
2.Inductance earthing(In practice in UN)
3.Using resonant coil
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / kishore
along with above said earthing thransformer bushing is also
earthed which is mandatory
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / hero
along with above said earthing thransformer plate earthing
is required
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / ravi nalli
Whether neutral (from neutral bushing) is connected tank
body is correct
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / manikandan
Now days in normal practice we are using 100mm Dia cast
iron pipe length of 2.5Mtr.It is good conductivity compare
the pipe and plate earthing.
| Is This Answer Correct ? | 0 Yes | 8 No |
how to calculate mf when meter and cTPT detail are given
AC covered area by ton calculation
what is the minimum requirement gigaohms for the insulation test using 5kv in 300mm xlpe cable
i want the formula of total eletical knowledgement
how to cal calculate capacitance in DC Circuit
What is OLTC AND RTCC and it's function?
What is a roll of adopter panel in terms of h.t. Panel ???
1 amp means-how many electron flow per second. ?
why we provided electrical earthing?
we are using three transformer 33000/430 vac for three separet block.all three transformer have three LT panel separetly. can be Interconnected all three panel through bus coupler. this is permissable or not by state electricity board.
can we keep open the secondary of current transformer?
should %impedance be high or low in a power transformer? if so why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)