how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?
Answers were Sorted based on User's Feedback
Answer / elangovan t
You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ashish
FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / aksx
how to find relay range and relay setting of three phase induction motor of 30kw ratting.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thakur
Full Load Current of Motor-52Ampas per(415.1.732.0.8)
Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)
Is This Answer Correct ? | 10 Yes | 13 No |
Answer / abhijit
as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sanjay
40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.
Is This Answer Correct ? | 9 Yes | 26 No |
we have one 75kw motor 380 volt 3ph amp134 please advise which size of cable required
how generater works
Equal resistance of 100ohm each are connected to the arms of whestons bridge, which is supplied by 2v battery. The galvanometer can sense a current low as 1microAmp. What is the smallest resistance that can be measered.
Please explain me about Relay curves and their sources to read ?
How do ACB are maintenance, what are the problem occurred in ACB
what is relation between vector group of transformer and its load hormonics?
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
how the BDV of the oil will be checked using moterised controled HV SET?
What is diversity factor in electric installations?
Please tell me the power flow from pmg to main rotor of an alternator (Including AVR unit)?
1.What do you mean by inductive and capacitive parts of an electric circuit. 2.What do you mean by decrease of inductane and capacitance of a network? Please dont give me the text book answer.3. What is class X ct and its applications?
What are the classification of Servo Motor?