hw to calculate flc of motor ? data are:3-phase,50Hz,30kw
Answers were Sorted based on User's Feedback
Answer / chetan & panks
Please mention voltage level & PF.
Assuming the voltage level 415V & PF 0.85,
FLC=kw/(ROOT3xkVxcoso)
= 30/(1.74x0.415x0.85)
= 48.87A
Is This Answer Correct ? | 52 Yes | 4 No |
Answer / pintoo
the data u have given is not sufficient to calculate the
FLC.
the exact formula to calculate FLC is:
P=sqrt(3)*V*I*cos(phi)*efficiency
I=P/[sqrt(3)*V*cos(phi)*eff.]
P=30KW=30000Watt
V=415V
cos(phi)=?
eff.=?
put the value of cos(phi) and efficiency then u will get
accurate FLC.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abhishek uppal
1H.P= 0.746 watts i.e power
so in 3 phase ,power =root3 *v*flc(Il)*cos phi
power =.746 watts
v=415v, and cos phi=0.8...so substituting above values
0.746=1.732*flc*415*0.8
so 7460/1.732*415*0.8= 1.31 A
So flc=1.31A...so accordingly,
find for 30 kw.
Is This Answer Correct ? | 8 Yes | 9 No |
Answer / x man
i will tellu a simple method,
hpx1.4 ..its an industrial method
Is This Answer Correct ? | 6 Yes | 8 No |
Answer / rajkumar r
U CAN FIND FLC OF THE MOTOR IN THE MOTOR NAME PLATE ITSELF.
MOREOVER,
1HP=0.746KW
1KW=1/0.746HP
30KW=30/0.746 HP=40HP
Practically current taken by 1HP motor=1.342A
so full load current of 30kw(40HP) motor=40*1.342=54A
Is This Answer Correct ? | 20 Yes | 32 No |
Answer / adnan
FLC : Can be Measured By their name Plate
Engr.adnan
Is This Answer Correct ? | 0 Yes | 13 No |
which bridge is used to measure frequency?
If there is no problem with the electronic circuit and regulator then why the motor start rotating at low value of regulator with full speed both at laod and no load??? and if my judgement of circuit is wrong then what is your openion?
A ray hit a smooth regular surface at an angle of 20 from the normal. Calculate : 1. The angle btw the incident and reflection ray. 2. The angle of deviation.
In the N-series schneider reclosers. What is the difference between current during fault time and current at tripping? This appears in the Event log in an event of a trip out.
In what voltage EHT works(133/132/33/66kv?
List few applications of d.c series motor?
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
transmission line losses
A 15 kw squirrel cage motor having a maximum efficiency of 90% on a continuous full load has temperature rise of 42 degrees celcius after 30 min and 52 degrees celcius after 1 hr under the above operation conditions. a) calculate its final steady state temperature rise on continuous load and the heating time constatnt. b) if the motor is operated on a short load for 9 min estimate its temperature rise. c) calculate the maximum overload that can be applied on a short, 9 min rating so that the temperature rise is the same as the final steady state temperature rise on continuous load.
we have two 11/.433 kv. distribution Transformer rating as 1000 kva & 500 kva , i wants to run parallel both transformer. both transformer impendence voltage is 5.24%, How can we run both t/f, & how sharing the load
how does a tube light starter works?