how to control the generator output voltage?
what r the condition should satisfy for synchronization?
Answers were Sorted based on User's Feedback
Answer / rajkumar r
By varying FIELD excitation we can control the output of DG.
Practically by changing AVR setting we can control the
output of DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. Speed/frequency should be the same
4. Load impedance should be the same.
Is This Answer Correct ? | 27 Yes | 3 No |
Answer / rvg.msceb
to be very clear, in commercial generator, nobody using
separated excitation system. self excitation is the best
method unless some specific reasons.
For controlling output voltage, a device called AVR,
automatic voltage regulator to be used, and it sense the
output voltage at each instance, and adjusts accordingly.
these are the condition for syncronization.
1.phase sequence of both generators should be same.
2-frequency shuld be same.
3-terminal voltage shuld be same.
4.both generators should have nearly same percentage
impedence.
Is This Answer Correct ? | 24 Yes | 1 No |
generator out put voltage is controlled by varying
excitatoin.
for syncronising of generator :
1 phase sequence should be same
2. voltage and frequency should be same and one most
important
3. phase angle should be same
Is This Answer Correct ? | 17 Yes | 4 No |
Answer / prembujju, park institutions
To control the output of the generator we have to consider the
following conditions
1. phase sequence will be same
2.terminal voltage will be same
3.frequency will be same,
if we change the speed of the prime mover we can get
controlled generator output. but fuel input increases which
changes the frequency also. so system not matches for those
three conditions.
on other hand the output of the generator can be
controlled by increasing or decreasing the excitation
depending of the load demands.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / pravesh
By varying FIELD excitation we can control the output of DG.
Practically but commertial d.g. sets are controlled by self
excitation and avr controls the output voltage output of
DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. frequency should be the same
4. percentage impedance should be the same.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / pavan
By varying the turbine speed. voltage, frequency & speed are
to be consider for synchronization.
Is This Answer Correct ? | 5 Yes | 19 No |
Answer / pradeep kumar rawat
by contoling the fuel we can contol the output voltage of
generator.
condition for syncronization.
1-phase sequence shuld be same.
2-frequency shuld be same.
3- terminal voltage shuld be same
Is This Answer Correct ? | 3 Yes | 24 No |
What is the role of a Production Engg in a Industry?????
what happens when the phase and earth wires comes in contact? and why
What is the reasonable voltage between Neutral & Earth of an electrical system for good earthing?
Why the suply frequency in INDIA is 50HZ
why in isolation transformer we dont get any shok?
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
0 Answers ABC, Reliance Life Sciences, TCS,
Can anybody tell me how to calculate(formula) earth flat size(for copper and aluminium).
How to calculate the actual 3phase power, if the load current of each phase is not balanced
how megger step up the DC voltage
If the field winding of the dc shunt motor is removed then what will happen to the motor ? will it turn or not
Differentiate AC and Dc resistance
What will happen if I apply DC to AC transformer? please send detailed answer at habib_rahman_habib786@yahoo.com