In any Industry, Which voltage level either 3.3kV or 6.6KV
to be chosen? Then I would like to know ,Is there any cost
consideration or Rating of motor?
Answers were Sorted based on User's Feedback
Answer / kapil narayanrao bahadure
In any Industry, voltage level either 3.3kV or 6.6KV its
not chose the motor ratings.voltage level in any industry
depend upon total load of industry.firstly total load of
industry consideration & after voltage level consider.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kunal
for cost consideration of motor: It is tradeoff.. now if
high voltage rating is selected less current will flow for
same load . this will save costs on copper but at the same
time cost of insulation will increase. .....if lower voltage
is chosen then higher currents will result for same load. so
higher cost of copper but reduced cost of insulation.
for consideration of voltage for industry depends on the
load. and if heavy loads are present usually higher volatges
are chosen as losses due to current are far more.
MW rated motors will always be run on higher voltages.
higher the better.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / veena
To choose the voltage level for any Load two factors has to
be considered one is the Total load and the distance of
transmission line .There is a formula to calculate the
economic transmission voltage
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rocks
6.6kv line.it also depend on the rating ot the motor that
is if high motor rating the vtg drop is siginifently more
than low motor rating.hence 606kv line is morepreffered in
industry
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / parth rawal
voltage level chosen 3.3kv due to insulation consideration
| Is This Answer Correct ? | 0 Yes | 2 No |
practically What is power factor
how to calculate lux level in out door (yard lighting) please expalin with a example
What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??
you have an automatic voltage regulator at home for your appliances,if the voltage in your area drops from 220v to 190v,does the output of the automatic voltage regulator drops?or does it retains the 220v output?
why various test are performed on electrical panels & power cables before commissioning on site & what are these test???
what is the purpose for open delta connection in potential transformer
Instead of single phase(220), if we apply Phase to phase (R&Y)supply (eg: for lighting fixture). what will be the power formula?
When the DG is running at the time we can connect to capacitor banK? why it is required or not
We in my plant one of the transformer showing neutral to earth voltage is 22V how to solve it
how i can calculate the size for fire cable
PLZ EXPLAIN CORONA,SKIN,BIRD PALE,SPAN,SAG Effects of power cable.
help me with the question that might be ask on the interview for technical position
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)